Ok, so here's my situation.
I am having a 30' x 50' x 12' workshop erected on the property I own and I need to get power to it.
I have determined that I will need 150 amp sub-panel out at the shop, which includes my anticipated future loads:
Three 240 volt loads (50 amp compressor, 40 amp welder, 40 amp A/C unit)
Three 20 amp loads (Five 8' Florescent lights per breaker)
One 15 amp breaker for lighting over workbench area
One 15 amp breaker for outside lighting/receptacles
Five 20 amp breakers for branch circuits (4 receptacles per breaker)
Does this sound like an appropriate load calc??
The problem:
The shop is ~400 feet from the meter pole. The way the electrical is set-up is that my meter loop is 200A which feeds the 200A panel inside our home.
What I think I need to do is upgrade the meter loop to a 300A panel, then run a 200A breaker to the house and a 150A breaker to the shop, does this sound reasonable or correct?
I believe, based on my rough voltage drop calc, I'm going to have to use 3/0 wire from the meter to the shop (~400 ft), does this sound correct?
I would run 3 3/0 wires through 2.5" conduit, not sure on the size ground; only two 90 degree turns in conduit.
I'm also going to have the concrete guy lay in grounding wire into the slab to connect to the shop sub.
This is kind of where I'm at, as pricing out the electrical stuff is the last step I need to price out. I'm confident that I can get the work done and the only thing I may hire out to an elctrician is to upgrade the box at the meter.
Thanks ahead of time for you input, questions, corrections, and so forth.
-Patrick
P.S. Having the utility come out and drop another meter by the shop is cost-prohibitive due to the monthly service charge, regardless of power used or not.
I am having a 30' x 50' x 12' workshop erected on the property I own and I need to get power to it.
I have determined that I will need 150 amp sub-panel out at the shop, which includes my anticipated future loads:
Three 240 volt loads (50 amp compressor, 40 amp welder, 40 amp A/C unit)
Three 20 amp loads (Five 8' Florescent lights per breaker)
One 15 amp breaker for lighting over workbench area
One 15 amp breaker for outside lighting/receptacles
Five 20 amp breakers for branch circuits (4 receptacles per breaker)
Does this sound like an appropriate load calc??
The problem:
The shop is ~400 feet from the meter pole. The way the electrical is set-up is that my meter loop is 200A which feeds the 200A panel inside our home.
What I think I need to do is upgrade the meter loop to a 300A panel, then run a 200A breaker to the house and a 150A breaker to the shop, does this sound reasonable or correct?
I believe, based on my rough voltage drop calc, I'm going to have to use 3/0 wire from the meter to the shop (~400 ft), does this sound correct?
I would run 3 3/0 wires through 2.5" conduit, not sure on the size ground; only two 90 degree turns in conduit.
I'm also going to have the concrete guy lay in grounding wire into the slab to connect to the shop sub.
This is kind of where I'm at, as pricing out the electrical stuff is the last step I need to price out. I'm confident that I can get the work done and the only thing I may hire out to an elctrician is to upgrade the box at the meter.
Thanks ahead of time for you input, questions, corrections, and so forth.
-Patrick
P.S. Having the utility come out and drop another meter by the shop is cost-prohibitive due to the monthly service charge, regardless of power used or not.