View Full Version : Evap coil froze up. Does it mean I am low on charge


racefan1
Jun 12, 2010, 07:30 AM
When we got home unit was a block of ice does it mean I am low on charge. Change filter regulary.also also recently it was 85 out and the unit ran constantly and neve got below 79

wmproop
Jun 12, 2010, 07:43 AM
Not always the answer,, is indoor fan blowing ? Is it blowing at proper speed? Could the evap-coil be in need of cleaning? The HVAC tech you need to come in to look system over should be able to determine

jdjohn84
Jun 12, 2010, 08:53 PM
Let the ice melt, then clean the coil by using a brush attachment on a vacuum. If it freezes again after that, call a tech.

wmproop
Jun 13, 2010, 09:30 AM
The coil needs to be cleaned from the underside,, the inside of the coil you can`t see until the end plate is removed so you can get to and see,, just vaccuming the outside isn`t getting the job done

jdjohn84
Jun 13, 2010, 06:39 PM
For mine I vacuumed the filter-side of the coil. Seems like it would be the dirtiest.

Joshdta
Jun 13, 2010, 07:39 PM
Most of the coils do not need cleaned, if you have a 90% furnace. If the dirt is anywhere it is stuck to the secondary heat ex and the blower will have to be pulled. Most likely you are low on freon.