dave-59
Mar 26, 2010, 06:52 AM
Hi according to the ugly book I just bought page 117 a separate building/structure supplied by feeder circuit shall have equipment grounding conductor sized iaw table 250.122 run with the supply conductors and connected to the building disconnecting means and grounding electrode. So what I gather from this now you have to run 4 wires in a trench. The ground and neutral is tied/bonded together in the panel boxes at both ends, along with the ground rods. Am I close? So if I plan to run a 100 amp feeder circuit, a 2-2-2-4 aluminum cable would be required? Thanks for the help. Dave