Jan 31, 2010, 08:50 PM
My out side unit has no power 24v to the contactor ,thermostat is new ,fuses breakers good ,no power to green wire on outside unit

hvac1000
Jan 31, 2010, 09:05 PM
You will have to trace the contactor wires back through any device attached and then back into the interior air handler until you find the part that is causing the problem. If the thermostat has been replaced and the problem started about that time I would look there first.

markevo1974
Feb 1, 2010, 04:59 PM
I should have mentioned I replaced the transformer also

hvac1000
Feb 1, 2010, 07:39 PM
As mentioned before you have your work cut out for yourself. Start tracing the wiring. You will eventually find the problem.

markevo1974
Feb 6, 2010, 12:36 PM
Yellow wire has 24 from thermostat,and is showing volts up to
Circuit board ,if I put 24volts to contactor system outside starts
Is crcuit board to blame