Jan 4, 2010, 08:56 AM
Having an issue that just started recently with our Carrier 58GP Series 100 furnace. At first it had the symptoms of a bad limit switch, furnace would turn off, blower off, then blower back on and off. I didn't replace the limit but am now having a different problem, the blower won't shut off (The flame will come on when it's supposed to).

I'm attaching the electronic schematics:

http://img51.imageshack.us/i/img1549p.jpg

I've done some troubleshooting and am almost certain that it's not the limiter. I've disconnected Lim-1 wire and Lim-2 wires blower remains on (no voltage on GH).

Just by looking at the schematics it seems to me the HFR or CFR relay is stuck on but I can't seem to get them to open.

What steps should I take now? Should I just buy a new control board?

Thanks

hvac1000
Jan 4, 2010, 09:23 AM
Your image file does not work at image shack.

Disconnect the G wire on the furnace therminal strip and run it. Report back. If this fails it might be the board.

jschen
Jan 4, 2010, 09:32 AM
I've disconnected all the thermostat wires to no effect. Looks like I'm going to go get a new board at lunch.

Good thing I posted the wrong link as it was the wrong photo anyway. =) Here's the right one.

http://img683.imageshack.us/img683/4906/carrier.jpg

jschen
Jan 4, 2010, 11:15 AM
Changed out the controller, seems to have done the trick.

hvac1000
Jan 4, 2010, 11:19 AM
Good deal. Glad you have heat