View Full Version : Trane furnace troubleshoot heating control


Luke Moncrief
Jan 3, 2010, 11:36 AM
TRANE MODEL: TUY060R9V3V3 SERIAL: Z313Y8F7G about 6years old.
Thermstat calling for heat. Furnace does not purge or heating come on. Red LED is blinking about 1 time per second. Green LED blinks much more slowly. Yellow LED's at G, Y, & YLO, do not light up.
5 amp fuse appears to be good.
I put new batteries in the thermostat, no change.
This is gas heat with an electric Air conditioner, not heat pump.
Tempered R & BK, no change.
Control is C341033P01 and labell inside furnace door panel say replace with CNT2536.? Don't understand why!
I powered down outside breaker to AC, and inside power switch , no change except I could hear relay drop out upon each "power off /power down".

hvac1000
Jan 3, 2010, 12:06 PM
Look on the back side of the blower motor access door for the blink/flash code legend

Luke Moncrief
Jan 3, 2010, 01:46 PM
Looks like a normal heating call and that would be good. However, the furnace does nothing else.
Please list next couple of troubleshooting items.
I guess ignighter or other safeties
Can you help more.
Thanks very much.

Luke Moncrief
Jan 3, 2010, 01:47 PM
Can you define further troubleshooting steps for me?
Thanks very much!

hvac1000
Jan 3, 2010, 02:02 PM
That unit has a variabble speed draft inducer along with a 2 stage gas valve. This unit is not used friendly to service since many of the parts have to be replaced since the original trouble prone items are NO LONGER available. I suggest you have on site service for your unit.

You can jump the thermostat out to eliminate it from the circuit for testing purposes .