View Full Version : Rpm motor out of range


xavia9
Nov 21, 2009, 09:44 AM
Have a carrier weather master and am getting the error message that my rpm motor is out of range.. the heater works if I have it set in emergency mode..

KC13
Nov 21, 2009, 10:36 AM
Airflow restriction can produce this fault. Check air filter and, if possible, air conditioning coil (if present) for blockage.

Joshdta
Nov 21, 2009, 10:42 AM
What would change the fault by putting it to emg heat? I agree must be a airflow problem!

KC13
Nov 21, 2009, 10:45 AM
what would change the fault by putting it to emg heat? I agree must be a airflow problem!The emergency mode selection (DIP switch on circuit board) defaults the unit to maximum values for requested blower & inducer CFM/RPM . This is usually effective as a short-term solution when a secondary HX is restricted.