View Full Version : How to calculate the short time current rating for current transformer?


pandees
Nov 2, 2009, 08:13 AM
Respected sir's,

Please clear my doubts?
How to calculate the "short time current rating"(i.e-primary short time current rating-like if u take 400-400/5-15va/class1,40ka/3sec).


40ka/3sec-how to calculate this rating from the substation?
Is there any formula?please advise me...

I am waiting for your's reply...


Thanks&regards,
pandees.b

anasmemon
Mar 10, 2011, 01:43 AM
Short time rating is defined by your MVA rating. Suppose you are using 0.8MVA transformer at 33/11KV, so your STC will be 0.8*1000/(1.73*11)=42KA.

I hope this will help you. So to calculate STC the data you have given is not useful.. but system parameters are required.

kkspwr
Jul 16, 2012, 11:00 PM
How much will be 6.6 /.4 kv transformer be equivalent in KVA

tkrussell
Jul 17, 2012, 04:50 AM
Not enough information provided, assuming you mean the primary is 6.6kV and the secondaray is .4 kV.


how much will be 6.6 /.4 kv transformer be equivalent in KVA

surajkr123
Jun 2, 2013, 09:40 PM
Study some electrical man , you are technically too weak to suggest , are you aware of % impedance?