fblankinship
Oct 27, 2009, 04:39 PM
I know all this is wordy but would appreciate someone in the know looking it over. We have a real stickler electrical inspector and want everything to be code. Thanks in advance.
I wired my barn without a permit and now want to get a permit. I thought I would explain how I wired it and ask you guys to check it over.
1. I ran the power from a main service panel located outside, it is a 200 amp feed through panel that also supplies my house. The house is also a 200 amp panel with a 100 amp fuse that feeds the internal house subpanel.
2. The run from the main panel to the barn is about 30 feet. I installed a 100 amp circuit breaker to feed the barn internal subpanel. I used #2 aluminum 4 wire (2hots, neutral and a insulated ground). I installed the wiring in a 11/4 schedule 40 electrical pvc (I used schedule 80 for the exposed portion with expansion fittings). The conduit is buried 18 inches (the ditch is still uncovered, I plan on covering the ditch halfway then putting a yellow danger tape down then completing the fill). I connected all this to a 100 amp subpanel located inside the barn. I grounded the subpanel with a #4 bare copper wire (I know it's large for the ground but I had the wire) I used 2 ground rods spaced about 61/2 feet apart. I did not bond the ground inside the panel.
Electrical Circuits
1. I used MC cable so the mice wouldn't eat the romex, all circuits are 20 amp with #12 copper wire (2 wire with a ground). I used steel 4x4 deep boxes for all recepticles, I grounded the steel boxes with ground wire clips hooked to all incomming ground wires. I used 3/8 inch steel clamps to attach the mc cable. I clamped the mc cable 6 inches from all the boxes and then at lease within 4 feet thereafter. All switches and GFI's are rated at 20 amp. The outside lights and GFI's are all in outside weather proof boxes, the GFI's also have the wet location covers. I have a total of 5 20 amp circuits in this 100 amp panel. I would like to hook up a 50 amp 220 circuit for my welder (after I get it inspected).
2. I ran one circuit for part of the lighting. The lighting circuit operates 4 florodex 85 watt lights on the inside (barn is 24x40 about 960sf) an outside light (2 ea 250 watt flood light) and a Halogen 500 watt light with motion control located over the double door. The inside lights and the 2 other lights I talked about are switched inside a 3 gang box located at the side door. The inside light is controlled with a 3 cay switch, the other 3 way is located at the back door (ran 3wire #12 with ground). The back door has a 2 gang box the other switch controls another outside light located by the back door ( I powered this other outside light from another 20 amp circuitis ( so I have 2 different power circuits in this 2 gang box).
3. The separate 20 amp circuit that I used for the outside light I talked about above also powers 1 outside gfi located at the rear of the building and 4 other duplex recepticles. This circuit has a total of 5 recepticles and 1 500 amp outside light circuit.
4. I have another 20 amp circuit that runs to a 2 gang box with 2 duplex 20 amp recepticles, I wanted a separate circuit for my freezer.
5. I have another 20 amp circuit that connects 4 inside duplex recepticles and one outside GFI (located on the side of the house).
6 I have another circuit that connects to 3 duplex recepticles and one outside GFI (located on the opposite side of the barn)
Any advice is appreciated Also, do I need to submit a wiring diagram when I fill out the permit?
I wired my barn without a permit and now want to get a permit. I thought I would explain how I wired it and ask you guys to check it over.
1. I ran the power from a main service panel located outside, it is a 200 amp feed through panel that also supplies my house. The house is also a 200 amp panel with a 100 amp fuse that feeds the internal house subpanel.
2. The run from the main panel to the barn is about 30 feet. I installed a 100 amp circuit breaker to feed the barn internal subpanel. I used #2 aluminum 4 wire (2hots, neutral and a insulated ground). I installed the wiring in a 11/4 schedule 40 electrical pvc (I used schedule 80 for the exposed portion with expansion fittings). The conduit is buried 18 inches (the ditch is still uncovered, I plan on covering the ditch halfway then putting a yellow danger tape down then completing the fill). I connected all this to a 100 amp subpanel located inside the barn. I grounded the subpanel with a #4 bare copper wire (I know it's large for the ground but I had the wire) I used 2 ground rods spaced about 61/2 feet apart. I did not bond the ground inside the panel.
Electrical Circuits
1. I used MC cable so the mice wouldn't eat the romex, all circuits are 20 amp with #12 copper wire (2 wire with a ground). I used steel 4x4 deep boxes for all recepticles, I grounded the steel boxes with ground wire clips hooked to all incomming ground wires. I used 3/8 inch steel clamps to attach the mc cable. I clamped the mc cable 6 inches from all the boxes and then at lease within 4 feet thereafter. All switches and GFI's are rated at 20 amp. The outside lights and GFI's are all in outside weather proof boxes, the GFI's also have the wet location covers. I have a total of 5 20 amp circuits in this 100 amp panel. I would like to hook up a 50 amp 220 circuit for my welder (after I get it inspected).
2. I ran one circuit for part of the lighting. The lighting circuit operates 4 florodex 85 watt lights on the inside (barn is 24x40 about 960sf) an outside light (2 ea 250 watt flood light) and a Halogen 500 watt light with motion control located over the double door. The inside lights and the 2 other lights I talked about are switched inside a 3 gang box located at the side door. The inside light is controlled with a 3 cay switch, the other 3 way is located at the back door (ran 3wire #12 with ground). The back door has a 2 gang box the other switch controls another outside light located by the back door ( I powered this other outside light from another 20 amp circuitis ( so I have 2 different power circuits in this 2 gang box).
3. The separate 20 amp circuit that I used for the outside light I talked about above also powers 1 outside gfi located at the rear of the building and 4 other duplex recepticles. This circuit has a total of 5 recepticles and 1 500 amp outside light circuit.
4. I have another 20 amp circuit that runs to a 2 gang box with 2 duplex 20 amp recepticles, I wanted a separate circuit for my freezer.
5. I have another 20 amp circuit that connects 4 inside duplex recepticles and one outside GFI (located on the side of the house).
6 I have another circuit that connects to 3 duplex recepticles and one outside GFI (located on the opposite side of the barn)
Any advice is appreciated Also, do I need to submit a wiring diagram when I fill out the permit?