I have a hydronic gas fired boiler I am trying to service this boiler has been off for at least one season that I know off I ran system return side was not returning properly so I started bleeding system shutting off valve before circulator pump connecting hose to above spikit and started draining but very little to none water came out I manually ran water threw system to push air out but only received a little more of water flow I ran for at least 30 min still cannot get proper return do anybody know how I can bleed this system problem properly
T-Top
Oct 15, 2009, 06:13 PM
Did you check to make sure the pump was running and that the impeller was not restricted with settlement? No air bleeder at the coil or coils?
jcapone2524
Oct 15, 2009, 06:20 PM
I didn't check pump or for coils yet I don't get it I'm forcing water threw system and only getting little water back when I should be pushing out air
T-Top
Oct 15, 2009, 06:26 PM
You got a bad restriction. You need to flush backwards through the system if you can to get it cleaned out.
jcapone2524
Oct 15, 2009, 06:30 PM
How cause this boiler doesn't have a valve after expansion tank to connect hose too
T-Top
Oct 15, 2009, 06:57 PM
That's a question for the person who installed it. Can the system be backed flushed? Your going to need to break the system down to find the restriction if not.
hvac1000
Oct 15, 2009, 08:39 PM
If the system has zone valves they have to be open to perform a flush OR fill the boiler system. Most zone valves have a manual lever or setting to allow this with power off.