View Full Version : 1995 Bryant 90i Plus won't ignite


JOAT65
Oct 12, 2009, 05:29 AM
Hi,

My furnace starts fan, pressure switches activate, gas valve turns on, but ceramic ignitor is not glowing. I changed the ignitor and no improvement. I measured the voltage on the plug with the ignitor disconnect during startup and only got 8 volts AC. Does this indicate that the control board needs to be replaced? Is there any other possibilities. The code is a 34.

Thanks

hvac1000
Oct 12, 2009, 06:44 AM
Code 34 = Ignition Proving Failure. If you look on the inside of the blower compartment door the code should be there on the wiring diagram.

You might try to clean the flame sensor with steel wool or sand paper.

JOAT65
Oct 16, 2009, 05:05 AM
Thanks for your input. The photos are very helpful.

svanbschalkwyk
Jan 22, 2011, 10:01 AM
I have ethge same problem : the voltage to my ignotor is something like 8 VAC.
Any ideas?