View Full Version : Coleman 7900 mseries furnance/mobil home


Barnabay
Oct 3, 2009, 05:34 PM
My furnace come on even though the stat is not wanting heat,the only way to shut it down is to manualy turn it off at the furnace

hvacservicetech_07
Oct 3, 2009, 05:58 PM
Remove the cover on the thermostat, make sure no wires are touching or shorted together. Remove the white wire from the W terminal, does that shut it off?

Barnabay
Oct 3, 2009, 07:07 PM
No,this does not do anything,the blower and burner come on,even when the stat is not connected

wmproop
Oct 3, 2009, 08:21 PM
Make note of where what color wire is connected to and disconnect the tstat wires at the furnace,, see if that stops it from running,, if it does you prob. Have shorted tstat wires, you might have to replace the wires to correct the prob. shouldn`t be to hard in a mobil home

hvacservicetech_07
Oct 3, 2009, 08:21 PM
Trace the low voltage wires, something is shorted.

Barnabay
Oct 4, 2009, 05:05 AM
Would a bad limit switch cause the problem?

hvac1000
Oct 4, 2009, 08:50 AM
If yours is the old style control system (a heat/off/cool switch on the furnace) one of the relays in the compartment is stuck in the heat on position.