Can somebody can tell me about the word "extinction pop: refer to

RickJ
Oct 19, 2006, 01:25 PM
This, like your other post, is more like "lingo" than terms professionals generally use.

I think that the term probably refers to a "flashback" or "pop" or "poof" that sometimes happens when you turn a burner off.

Where are you hearing or reading about these terms?

NorthernHeat
Oct 19, 2006, 02:33 PM
It is when the flame goes back into the burner when the gas valve closes. It is more prominent in LP furnaces and specific burner designs

LPtrainer
Nov 21, 2013, 01:15 PM
Extinction pop is a little different from flashback, but sometimes the two symptoms occurs on the same gas burner.
* Extinction pop most often occurs on propane appliances. The primary cause is reduced gas velocity. The lower velocity causes a lower flame speed atop the burner allowing the flame to drop back inside the burner as the valve shuts down.The rich fuel then expands back to a combustible mixture and the hot burner reignites than small amount of trapped gas. It is not a safety issue.
In a new appliance this can be caused by too low a gas pressure, or excessive primary air, rectify by correct adjustments. But in an older appliance, it is often due to enlargement of burner ports over time, requiring the burner be replaced.
* Flashback generally occurs on a cold burner, when the gas pressure is out of specification required to obtain the correct velocity to propel the gas upward from the burner at the instant of ignition. Thus the gas/air mix in the burner is ignited and the force blows the incoming gas back to the orifice and the flame burns at the air shutter accompanied by a fluttering undersized flame atop the burner, a yellow flame at the air shutter and a loud fluttering noise. The poor combustion also produces a strong aldehyde odor.
If this occurs often, this is generally solved by bringing the gas pressure and air shutter setting into specifications, it is important to address, because burning at the orifice will fill the burner with soot and can cause safety issues to develop. However, if only an occasional occurrence, there is an issue with cold air pressure I the vent of a heating appliance that occasionally causes extreme pressure on the burner which is overcome as the exhaust draft is established.