We just bought a house with radiant heat. This is our first experience with that type of heating system. It is wired to have 3 different areas in the house with their own thermostats. They're very basic thermostats, and I would like to change them out for digital programmable thermostats to regulate the heat better in the house. Is there a certain type of thermostat I have to use with this type of sysytem?
We have a Burnham Series 2 (model b) gas-fired boiler. Thanks so much! -Jen :confused:
rickdb1
Oct 19, 2006, 09:44 AM
Hi there,
We just bought a house with radiant heat. This is our first experience with that type of heating system. It is wired to have 3 different areas in the house with their own thermostats. They're very basic thermostats, and I would like to change them out for digital programmable thermostats to regulate the heat better in the house. Is there a certain type of thermostat I have to use with this type of sysytem??
We have a Burnham Series 2 (model b) gas-fired boiler. Thanks so much!! -Jen :confused:
Nope. Any heating thermostat will work, Digital or not... Good idea to save money using the programmable T-Stat...
labman
Oct 19, 2006, 10:30 AM
It is not that simple. Search this forum, and you will find many threads where people are having trouble making programmable thermostats work. Much of the time, it is their own fault, or the thermostat is bad. Many of the problems are with a Honeywell RTH230. Let me give you some background.
Usually there is a 24 volt AC transformer in the furnace with the secondary winding connected to a red wire running to the thermostat and a blue wire, common, to the gas valve, A/C relay, and fan relay. From the thermostat there will be white wire to the gas valve, yellow to the A/C, and green to the fan. The thermostat is wired to switch the power from the red to the white, yellow, and green as needed with the blue completing the circuit. Most thermostats and furnaces have the contacts labeled R, B or C, W, Y, and G for the corresponding wire colors. It may be wired to have the A/C control wires return to the furnace and its controls and then a second wire goes to the A/C unit. Internal wiring may replace the green wire if the thermostat does not give you the option of fan only or continuous fan. Digital or programmable thermostats may need the blue wire connected to them.
That is for gas, forced air. A hot water system will be much the same at the thermostat except the fan on function won't work. When a zone thermostat calls for heat, 2 things must happen, the zone valve must open, and the boiler must come on if not already. If you don't have air, the old thermostats could be wired up with only 2 wires. Check, may be easier to see at the boiler, and don't buy a thermostat that requires the third wire to the common terminal. Other than that, make sure the thermostat comes with directions in English, and you follow them. Also, note where the wires were connected to the old thermostat. Doing those will avoid most of the problems I have seen here.
rickdb1
Oct 19, 2006, 12:46 PM
Assumed it was heat only on the circuit... Should be a snap... Red/White...
tkrussell
Oct 19, 2006, 12:53 PM
Finally, someone asking for advice BEFORE they take the existing stat apart and not knowing how it was wired, or if it is compatible with your system and wiring.
Note the model number , and a photo of inside and out if necessary, to a heating/cooling supply house or distributor. They will help you with choosing the right one to replace your existing stat.
Every distributor has at least one person that is a wiz at control wiring. Now you have someone to call to help with questions you may have if there is a problem.