cbella
Oct 13, 2006, 07:21 AM
Hi,

I live in a condo and have a Whalen Heat Pump. I changed the thermostat to a Noma digital programmable model (model # 52-255808) in the summer time. The A/C works well and the fan works well, but I did not test for heat as it was summer when I installed it.

Well, now that the weather is getting cold, I am not getting any heat! I am wondering maybe I did not wire the thermostat properly.

There are 4 wires: Red, Green, Yellow and Blue.

So, I connected them as follows:

Red - RH (RC and RH has a jumper on it)
Green - G (it says Fan Relay on the diagram)
Yellow - Y (it says Cooling Relay on the diagram)
Blue - W (it says Heating Relay on the diagram)

I shorted the Red and Green wire and the fan does come on. I did the same for the Red and Yellow wire and the air comes on. But when I shorted Red and Blue I hear a click but nothing else happens.

Please help. It's freezing in my unit.

Thanks in advance!

cbella
Oct 13, 2006, 12:52 PM
Can someone confirm that the Blue wire should be connected to the 'W' terminal?

I'm thinking maybe the Blue wire should not go to the 'W' terminal.

Thanks!

tkrussell
Oct 13, 2006, 01:00 PM
Process of elimination means the blue is for the heat, and should get connected to the W terminal. When you shorted the blue to red, and something clicked, it may take a few minutes for your heat to actually start.

Let it run a while, if the heat stll does not start, then there is a problem with the heating unit.

Kender
Oct 13, 2006, 07:45 PM
Are you sure that it is a heat pump? If so try connecting all four wires together. R-power, G to turn on the fan, Y to turn on the compressor, and B for the revercing valve to reverce the flow of freon. If that works then that t-stat will not work on heat pumps.

If it is not a heat pump then your wiring is correct. Try turning the fan to ON then turning on the heat. Some systems will not turn on the heat with out the fan being "ON" like Trane air handlers not sure about whalen. If that works than there should be a gas elect switch that needs to be changed on the t-stat.

NorthernHeat
Oct 14, 2006, 10:06 AM
Hi,

I live in a condo and have a Whalen Heat Pump. I changed the thermostat to a Noma digital programmable model (model # 52-255808) in the summer time. The A/C works well and the fan works well, but I did not test for heat as it was summer when I installed it.

Well, now that the weather is getting cold, I am not getting any heat! I am wondering maybe I did not wire the thermostat properly.

There are 4 wires: Red, Green, Yellow and Blue.

So, I connected them as follows:

Red - RH (RC and RH has a jumper on it)
Green - G (it says Fan Relay on the diagram)
Yellow - Y (it says Cooling Relay on the diagram)
Blue - W (it says Heating Relay on the diagram)

I shorted the Red and Green wire and the fan does come on. I did the same for the Red and Yellow wire and the air comes on. But when I shorted Red and Blue I hear a click but nothing else happens.

Please help. It's freezing in my unit.

Thanks in advance!
I've never seen a heatpump that operates on just 4 wires. But after 20 years of service work I've never heard of a Whalen either. Or a Nora. Look in the installer set-up book for the thermostat. You will need to get into the program mode and tell it that it is a heat pump, and weather the reversing valve is actuated on cooling or heat. Do you live in a very warm climate where an emergency heat source is unnecessary?

cbella
Oct 15, 2006, 08:29 AM
Thanks to everyone who responded. The issue is now resolved and here's what we did to resolve it:

Blue wire connects to 'B' terminal
Yellow wire connects to 'Y' terminal
Green wire connects to 'G' terminal
Red wire connects to 'RH' terminal

By default, there is a jumper on RH and RC, leave that as is.
There is also a jumper on HG, leave that as is.

To add:
Get a very short wire to create a jumper on 'Y' and 'W' terminal.

Turn thermostat on to Heat and it works!

NorthernHeat
Oct 15, 2006, 08:38 AM
Glad to hear you got it figured out. The blue wire must be for the reversing valve. Did you check and see that the A/C also works correctly?

cbella
Oct 18, 2006, 08:19 AM
Yes, I've confirmed that a/c works as well!

Thanks!

df186
Oct 10, 2010, 10:52 AM
OMG!! You guys just saved me a TON of cash.. This fixed my issue!! Thanks sooooo much!!

I have the same Heat Pump and I was having the same issue.. this is my config:

Black wire connects to 'Y' terminal (installer reversed the wires)
Yellow wire connects to 'W' terminal
Green wire connects to 'G' terminal
Red wire connects to 'RH' terminal

By default, there is a jumper on RH and RC, leave that as is.

To add:
Get a very short wire to create a jumper on 'Y' and 'W' terminal.

Turn thermostat on to Heat and it works as well as Cool!

Oh, and used the Honeywell RTH2310B Programmable Thermostat

df186
Oct 10, 2010, 01:01 PM
OMG!!!!!!! You guys just saved me a TON of cash.. This fixed my issue!!! thanks sooooo much!!!!

I have the same Heat Pump and i was having the same issue.. this is my config:

Black wire connects to 'Y' terminal (installer reversed the wires)
Yellow wire connects to 'W' terminal
Green wire connects to 'G' terminal
Red wire connects to 'RH' terminal

By default, there is a jumper on RH and RC, leave that as is.

To add:
Get a very short wire to create a jumper on 'Y' and 'W' terminal.

Turn thermostat on to Heat and it works as well as Cool!

Oh, and used the Honeywell RTH2310B Programmable Thermostat

Opps.. spoke too soon... so this doesn't work.. it doesn't seem to switch the flow from cold to heat.. it only gets stuck on one..