PDA

View Full Version : Wiring SPA/Hot tub


brian421
Jun 19, 2009, 08:29 AM
I am contemplating installing a SPA on my back patio slab. My 150 ampere panel is about 100 ft away. My plan is to run 6/3 along my outside eave (does this need to be in conduit?) and down an outside wall to the sub panel, because I live on a slab and do not have any other choice. My dilemma is once I get the feed to the sub panel (with 50 amp GFCI) I have to get it across 12' of concrete slab to the tub location. What are my choices with this? Can I run conduit across the slab? Ugly but I am not sure what other solutions there are.

Thanks

Brian

tkrussell
Jun 19, 2009, 10:51 AM
My plan is to run 6/3 along my outside eave (does this need to be in conduit?)

Whatever you use must be rated for wet location. NM-B Romex cable is not allowed in this location. Either UF cable, MC cable, or conduit with pulled THHN/THWN conductors will be allowed.

Conduit would look the best, I think.




, because I live on a slab and do not have any other choice. My dilemma is once I get the feed to the sub panel (with 50 amp GFCI) I have to get it across 12' of concrete slab to the tub location. What are my choices with this? Can I run conduit across the slab? Ugly but I am not sure what other solutions there are.


In this case where conduit must lay exposed on a slab, it will be subject to physical damage. Either steel rigid conduit or PVC Schedule 80 will be allowed.

brian421
Jun 19, 2009, 10:56 AM
Whatever you use must be rated for wet location. NM-B Romex cable is not allowed in this location. Either UF cable, MC cable, or conduit with pulled THHN/THWN conductors will be allowed.

Conduit would look the best, I think.




In this case where conduit must lay exposed on a slab, it will be subject to physical damage. Either steel rigid conduit or PVC Schedule 80 will be allowed.

What is MC cable?

tkrussell
Jun 19, 2009, 11:00 AM
See:

http://www.alliedeg.com/pdf/afc_mcsteel.pdf

brian421
Jun 19, 2009, 11:13 AM
Thanks, you have been a tremendous help. If my hot tub is rated at 50 amps what is the minimum wiring I can use? 6/3?

tkrussell
Jun 19, 2009, 11:21 AM
Yep.

tkrussell
Jun 19, 2009, 01:33 PM
I meant to mention this before, what is the chance of saw cutting the slab and chipping out a trench to lay conduit into, and avoid the physical damage issue, and a serious tripping hazard?

brian421
Jun 20, 2009, 06:11 AM
I meant to mention this before, what is the chance of saw cutting the slab and chipping out a trench to lay conduit into, and avoid the physical damage issue, and a serious tripping hazard?

If I do cut the slab am I still required to go 18" deep (I am in South Jersey).

stanfortyman
Jun 20, 2009, 08:10 AM
No, only 4" of concrete is required above PVC outside.

Also, you cannot use UF cable for any of the outside portion of this wiring, and any MC cable you use must be "listed for the location". They do sell underground MC cable but it is near impossible to fine, at least in most parts of the US.

brian421
Jun 21, 2009, 06:48 AM
No, only 4" of concrete is required above PVC outside.

Also, you cannot use UF cable for any of the outside portion of this wiring, and any MC cable you use must be "listed for the location". They do sell underground MC cable but it is near impossible to fine, at least in most parts of the US.

So if I use conduit what can I run? Can I run 6/3 NM inside and through conduit (shed 40 or 80) outside?

tkrussell
Jun 21, 2009, 07:05 AM
Do not pull NM through exterior conduit, not allowed as NM is rated for dry locations only.

Pulling NM, esp #6-3, is not done other than a short sleeve through walls or for protection. Conduit needs to be grossly oversized to handle NM cable.

PVC Sch 40 is fine. Need to check local codes as many require steel as PVC rises out of concrete.

Not sure where Stan came up with 4 inch covering over conduit. Table 300.5 of the NEC allows a min of 2 inch,althou deeper is better.

You could do this run entirely in PVC Sch 40, even where exposed under th eave.

Horizontal runs of PVC need added straps, as PVC sags. Long runs, esp when exposed to sunlight, need expansion couplings, as PVC expands and contracts greatly.

brian421
Jun 21, 2009, 07:09 AM
Do not pull NM thru exterior conduit, not allowed as NM is rated for dry locations only.

Pulling NM, esp #6-3, is not done other than a short sleeve thru walls or for protection. Conduit needs to be grossly oversized to handle NM cable.

PVC Sch 40 is fine. Need to check local codes as many require steel as PVC rises out of concrete.

Not sure where Stan came up with 4 inch covering over conduit. Table 300.5 of the NEC allows a min of 2 inch,althou deeper is better.

You could do this run entirely in PVC Sch 40, even where exposed under th eave.

Horizontal runs of PVC need added straps, as PVC sags. Long runs, esp when exposed to sunlight, need expansion couplings, as PVC expands and contracts greatly.



So for conduit my only option is THNN? Can't I use 1" conduit for 6/3 NM or UF?

tkrussell
Jun 21, 2009, 07:15 AM
NM is not allowed in exterior conduit. Exterior conduit is a wet location.

UF cable is rated for wet location.

If you insist to pull cable through conduit, do it at your own risk.

You will be sorry for trying, unless the conduit is oversized, even then there will be problems.

Wire pulled through conduit can be individual conductors with THHN/THWN, be sure it is rated THWN, or XHHW.

stanfortyman
Jun 21, 2009, 09:13 AM
Not sure where Stan came up with 4 inch covering over conduit. Table 300.5 of the NEC allows a min of 2 inch,althou deeper is better.
NEC T300.5, Column 3, fourth row down.

The 2" number is in row 2 and let's you go to 12" instead of 18" if there is 2" of concrete above it.

tkrussell
Jun 21, 2009, 09:28 AM
I am using Note #2 at the bottom. If saw cutting into concrete slab, I assumed there there will be concrete below, because of only chipping out 2 inch PLUS the diameter of the conduit ( added for clarification to the poster) and pour 2" above creating the envelope.

If the slab gets cut completely thru to earth, for some reason, then the conduit could be 12" deep providing there is a min of 2" of concrete above.

In any case, this is going to be a tough install for a hot tub.

stanfortyman
Jun 21, 2009, 09:40 AM
I see that note, but never thought it applied to PVC. I have no idea what they mean by "Raceways approved for burial only".
I see what you mean though by "concrete encased" and "envelope" as opposed to row four which refers to "under" a 4" slab.

Either way, I do agree with you.

brian421
Jun 22, 2009, 05:40 PM
So for conduit my only option is THNN? Can't I use 1" conduit for 6/3 NM or UF?

Another question... can I splice (through a J box) THHN and NM in my attic to avoid having to run conduit indoors?

tkrussell
Jun 23, 2009, 02:48 AM
Sure can, probably need an 8" x 8" x 4" JB.

brian421
Jun 23, 2009, 04:51 AM
Thanks, you have been a tremendous help!:)