View Full Version : Wiring blower motor relay


rickster558
May 24, 2009, 08:53 PM
My blower motor relay burned out and I replaced it with a universal relay. It has R, G, W, Y, and C. I got the wiring right for the furnace but I don't know where the wires for the air compressor go. The wires from the compressor are red, white, green and blue. I put the red wire on the W and the red on the Y. Blower starts on furnace when I turn thermostat on cool but compressor does not kick on. Any suggestions?

T-Top
May 24, 2009, 08:59 PM
Turn the power off to the outside unit remove the cover and see what wires are being used. You replaced more than a blower relay if you had to disconnect that many low voltage wires.

rickster558
May 24, 2009, 09:08 PM
The red and white wire are being used. The green and blue are routed to another box and are not connected to anything

rickster558
May 24, 2009, 09:10 PM
Sorry the post says I hooked the red wire twice. It was supposed to say the red is hooked to the Y and the white is to the C

T-Top
May 24, 2009, 09:17 PM
The only simple thing left to do is make sure the breaker is on going to the A/C unit.

rickster558
May 24, 2009, 09:20 PM
Does the wiring sound right to you? Red to Y white to C?

T-Top
May 24, 2009, 09:26 PM
Yes with just two wires it will not make a difference. They are not polarity correct. They can go either way.

KC13
May 25, 2009, 05:50 AM
I put the red wire on the W and the red on the Y.

Check your wiring again. Did you connect outdoor unit circuit to "Y" and "W", or "Y" and "C"? The second combination is correct.