Paris2
May 1, 2009, 11:01 AM
I am about to install a sub panel. I purchased a 125 amp panel but the vendor only had a 100 amp breaker to feed my panel from the main panel. Would this be within tolerance?

tkrussell
May 1, 2009, 11:13 AM
Yes, what you plan is fine. The panel is rated 25 amps more than the breaker feeding it. No problem.

sathe1963
May 2, 2009, 04:59 AM
Generally, upstream circuit breaker or isolator shall be of higher rating than the down stream breaker. In your case if both the switches / isolating points are in near by area, there is no problem. (becasue of any fault in your panel; only 1 no. 100 ampere breaker is going to trip. You should put a warning sticker on your 125 ampere breaker that "to be loaded up to 80 ampere only") this is because you are receiving power from 100 ampere breaker.