PDA

View Full Version : How to design a DG according to load


suniljayarajan
Apr 11, 2009, 03:18 AM
I want to know how to design a Generator

If suppose I need 480v; 3phase; 60hz

What is the KVA of DG
And how can I calculate

sathe1963
Apr 18, 2009, 08:37 AM
Dear Sir,

One has to look into max.inrush current capacity of DG set and parallelly, how much is the load. Next is what is the max kw capacity of load which would be started on genset when all other loads are ON.

suniljayarajan
Apr 18, 2009, 09:18 PM
It load is coming around 300A

sathe1963
Apr 18, 2009, 10:29 PM
Dear friend,

Apparently, you require 250 kva dg set. This could serve around 300 ampere load at 480 volts. + additional safe margin @ 20% to be considered according to standard rating available above the said rating. (one has to see that dg would feed to max. Capacity load when other loads are running and also to see that it is not under utilised... under loaded considering high running cost.