View Full Version : Wire size for a 100 amp sub panel 200 feet away
jordanmc1019
Mar 14, 2009, 09:37 AM
I have a 200 amp main panel in my house and I just built a garage and am planning on putting a 100 amp sub panel in the garage. The garage is about 200 feet from my house and it has a 2 inch pvc stubbed out underground. I am wondering what size aluminum I would need to feed it, and if I can use a smaller pvc.
jordanmc1019
Mar 14, 2009, 11:05 AM
I should add that the garage is detached and that I have a 50 amp 240 V welder and a 30 amp 240 V lift and there will be some convenience outlets and lights.
Tev
Mar 14, 2009, 11:14 AM
You would need 2/0 aluminum. Your equipment grounding conductor can be 6 AWG aluminum or 8 AWG copper. 2 inch PVC is the correct size for the three 2/0 THWN wires and the grounding wire.
stanfortyman
Mar 14, 2009, 11:49 AM
#2cu or 1/0al is all you need. Even that is considering a full time load of 80 amps, which you are likely never to see.
jordanmc1019
Mar 24, 2009, 02:48 PM
#2cu or 1/0al is all you need. Even that is considering a full time load of 80 amps, which you are likely never to see.
What size ground would I need
stanfortyman
Mar 24, 2009, 03:13 PM
Normally a #8 ground would be correct, but since you are increasing the size of the feeder you must also increase the size of the ground.
Without doing all the calculations I think a #6cu would be fine.
jordanmc1019
Mar 31, 2009, 07:22 AM
Normally a #8 ground would be correct, but since you are increasing the size of the feeder you must also increase the size of the ground.
Without doing all the calculations I think a #6cu would be fine.
Does my neutral need to be the same size as my current caring conductors
jordanmc1019
Mar 31, 2009, 07:23 AM
Does my neutral need to be the same size as my current caring conductors
If not what size could it be
KISS
Mar 31, 2009, 08:14 AM
Having the neutal the same size as the current carying conductors basically means that the entire 200 A at 120 is being fed from one side of the panel.
The neutral can be reduced by the 240 volt loads. e.g a 50 A 240 V load, can be take off 50 A at 120 V since the neutal will be 0 for this load. So, you could deduct 80A @ 120 V from the total. These loads are not continuous, so you can even deduct more.. 1.25 * 80.
You would have to look at the other stuff too.
If you went with the same neutral size, then you could have 100 A of 120 from one leg and 100 A from the other at 120V. With a lower neutral size, the you can't.
The neutral carries the difference of the two hots.