dport2009
Feb 22, 2009, 12:53 PM
Hi all,
I have a York Stellar, model # P3CCD08N04501A I think it's a early 90's model. I have had an issue with it short cycling during heating, I have watched the sequence of events, here is what I see.
1) Tstat calls for heat, usually it is very cold in the house due to no heating
2) inducer runs
3) HSI glows, about 35 sec
4) 30 sec in, gas valve actuates
5) flame on, stays on
6) about 70 to 90 sec later blower fan comes on
7) heat blows from registers for about 5 min, usually enough to raise temp in house by 1 or 2 degrees F
8) gas valve shuts off
9) HSI tries to reignite, gas valve will not actuate
10) control attempts 2 more times then control led flashes continuously
11) I turn power off and let it sit for at least 30 min, then try again, same sequence
I had a service repairman come out and had tested the flame sensor and HSI. He said that they checked out fine. I removed the flame sensor and cleaned, same problem.
The control P# White Rodgers 50E47-070
fan limit P# L4064Y1433 Honeywell has an internal by metal heater, no adjustment for fan on, just fan off and high cutout set around 200F
Gas valve P# 36E01 24VAC 1/2 X 1/2
When I tested the voltage during the 3 attempts before control lockout, control never sent voltage to the gas valve, (even though HSI was on) I had voltage at the press switch and across the flame rollout switch, I had 24VAC at the control on terminal TH during the failed retries. Not sure what is happening, if I try to cycle the power to reset it won't work 3 attempt and fail, but if turn power off for at least 30 min it will refire with same results as list above.
Thanks for any help you can provide
I have a York Stellar, model # P3CCD08N04501A I think it's a early 90's model. I have had an issue with it short cycling during heating, I have watched the sequence of events, here is what I see.
1) Tstat calls for heat, usually it is very cold in the house due to no heating
2) inducer runs
3) HSI glows, about 35 sec
4) 30 sec in, gas valve actuates
5) flame on, stays on
6) about 70 to 90 sec later blower fan comes on
7) heat blows from registers for about 5 min, usually enough to raise temp in house by 1 or 2 degrees F
8) gas valve shuts off
9) HSI tries to reignite, gas valve will not actuate
10) control attempts 2 more times then control led flashes continuously
11) I turn power off and let it sit for at least 30 min, then try again, same sequence
I had a service repairman come out and had tested the flame sensor and HSI. He said that they checked out fine. I removed the flame sensor and cleaned, same problem.
The control P# White Rodgers 50E47-070
fan limit P# L4064Y1433 Honeywell has an internal by metal heater, no adjustment for fan on, just fan off and high cutout set around 200F
Gas valve P# 36E01 24VAC 1/2 X 1/2
When I tested the voltage during the 3 attempts before control lockout, control never sent voltage to the gas valve, (even though HSI was on) I had voltage at the press switch and across the flame rollout switch, I had 24VAC at the control on terminal TH during the failed retries. Not sure what is happening, if I try to cycle the power to reset it won't work 3 attempt and fail, but if turn power off for at least 30 min it will refire with same results as list above.
Thanks for any help you can provide