View Full Version : Luxaire burner won't start
jbench
Feb 7, 2009, 07:42 PM
My luxaire furnace won't fire up. When I open the bottom panel and flip the pressure swith over and over, it tries for about 1 second to run
hvac1000
Feb 8, 2009, 05:58 AM
Exact model number of furnace?
jbench
Feb 8, 2009, 09:54 AM
Mdl# g8t11516uhc11a
s/n# ekjm466306 when I flip the pressure switch on and off repeatedly, it tries to start up for a split second
Thanks
KC13
Feb 8, 2009, 10:18 AM
I think you are referring to the interlock switch behind the blower access panel. The pressure switch is typically connected to the draft inducer via a small rubber hose. Sound right? Try this: Pull one of the wires off the PRESSURE SWITCH, then try to start the unit again. If it runs longer than before, the P/S is stuck in the closed position. Are there any status LED's on the unit?
jbench
Feb 8, 2009, 03:57 PM
I did mean the switch behind the access panel.
When I flick it on and off, it sometimes tries to start for a split second
KC13
Feb 8, 2009, 04:41 PM
The interlock switch is interrupting and restoring the power supply when you disengage and engage it. Did you... try... my previous suggestion?
jbench
Feb 8, 2009, 06:08 PM
There is a red status light behind the access panel and the guide says if flash once then off then lockout caused by flame sensed... when there should be no flame
mygirlsdad77
Feb 8, 2009, 07:03 PM
Does the flame ever come on?
jbench
Feb 8, 2009, 07:17 PM
No flame ever
KC13
Feb 9, 2009, 04:37 AM
Check flame sensor circuit for short to ground. Check circuit board for evidence of exposure to moisture (odixe trails, circuit path bridging).