Jan 24, 2009, 11:13 AM
Hi:
I had some renovations done and it seems like the thermostat was not properly connected and there is no heat. There are 3 sets of wires in the box. The termostat is dual pole with
L1, L2, T1, T2 connections. It was wired L1 and T2.
When I test the Thermostat with OHM meter it only measures continuity when turned on and at position L1 and T1.
I turned off the breakers and found when I connect the 2 wires at the thermostat together and check continuity at the heater - it check out OK.
So I suspect that the wires on the thermostat should be connect to L1 and T1 and not as originally done.
Thank you for your help