View Full Version : Dual pole thermostat wiring as single pole


nagy1106
Jan 24, 2009, 11:13 AM
Hi:

I had some renovations done and it seems like the thermostat was not properly connected and there is no heat. There are 3 sets of wires in the box. The termostat is dual pole with
L1, L2, T1, T2 connections. It was wired L1 and T2.

When I test the Thermostat with OHM meter it only measures continuity when turned on and at position L1 and T1.

I turned off the breakers and found when I connect the 2 wires at the thermostat together and check continuity at the heater - it check out OK.

So I suspect that the wires on the thermostat should be connect to L1 and T1 and not as originally done.

Thank you for your help

nagy1106

stanfortyman
Jan 24, 2009, 11:30 AM
So I suspect that the wires on the thermostat should be connect to L1 and T1 and not as originally done.

You are absolutely correct.

Line to L1
Load to T1