View Full Version : What size of braker do I need?
franco0783
Jan 20, 2009, 09:29 PM
What size of braker do I need if I have a size 10 wire for A/C
MarkwithaK
Jan 20, 2009, 09:31 PM
If you look on the information plate one the side of your condensing unit it should list the maximum current protection for your specific unit.
codyman144
Jan 20, 2009, 11:37 PM
To elaborate on what mark said, the breaker needed and wire size required depends on how many Amps the unit is rated for (draws).
For Example 15 Amps requires at least # 14
20 AMP at least # 12
30 AMP at least # 10
So if you know you need size 10 wire odds are unit draws a max of 30 Amps. But like he said it should tell you on the unit how many Amps it requires. Wire accordingly.
For simplicity I am leaving out voltage drop considerations, but if the unit is a sizeable distance from the service panel you may need bigger wire. How far away is it?
MarkwithaK
Jan 21, 2009, 09:37 PM
Most condensing units will tell you what the min. ampacity rating is as well as the max. fuse protection size.