Jan 19, 2009, 12:06 PM
Sometimes when I have the furnace set on automatic it will not turn on when the temperature goes below the set point. All I have to do in order for it to work again is turn the furnace off then back on (I do this at the thermostat) and it will work fine for a day or two, then the same thing happens again. Is it the Thermostat?

Any and all help would be appreciated!!

hvac1000
Jan 19, 2009, 01:11 PM
Brand of furnace?
Exact model number of furnace?
Brand of thermostat?
Exact model number on thermostat?

twilley
Feb 21, 2009, 08:52 AM
Sorry it has taken me a while to respond. The reason for this is because right after I posted the question the problem stopped. But the problem has started up again. Here are the answers to you questions:

Brand of furnace- Ruud Deluxe 90 Plus
Exact model number of furnace- UGED-06EMAES
Brand of thermostat- Honeywell
Exact model number on thermostat- T87F 23943 (I believe this is the model # as it was one of two #'s on the thermostat)

It seems that problem only occurs when it is realativley cold outside (below freezing).

Thanks for your time,
Danny

KC13
Feb 21, 2009, 09:33 AM
Does the circuit board on the furnace have a diagnostic LED? If so, check it the next time you experience this problem. Usually, a label describing the fault code translation can be found on the access panels of units equipped with self-diagnostics.

twilley
Feb 21, 2009, 01:30 PM
Thanks for the reply. I checked and do not believe the unit has a diagnostic LED. The unit is older maybe 10-15 years if that helps. You should also know that the thermostat is a non-electronic mercury dial thermostat.

Danny

KC13
Feb 21, 2009, 01:34 PM
If the action of switching the thermostat off/on causes the system to work again, the selector switch may be worn/oxidized. Mercury, eh? Sounds like it's time for a new one anyway. Even if it doesn't solve the problem, it's still a good investment and riddance of a hazard.

twilley
Feb 21, 2009, 01:41 PM
I am not 100% sure it is mercury but it sure looks like it. Can you give me an indication of where the selector switch is located?

Thanks again for your help.

KC13
Feb 21, 2009, 02:36 PM
On the thermostat (heat/off/cool).

mygirlsdad77
Feb 21, 2009, 05:07 PM
I would start by replacing the thermostat, it may not solve the problem, but if will eliminate the thermostat as the problem. If you have an older Honeywell t87f thermostat, then is is most likely mercury. The coiled spring has most likely worn out, causing problems with accuracey. Try turning the thermostat all the way up next time the furnace fails, if it comes on, then you have a bad thermostat. If it doesn't, the problem is most likely somewhere else, but I would replace therm anyway. Please let us know how things work out.

twilley
Feb 22, 2009, 06:19 PM
If the action of switching the thermostat off/on causes the system to work again, the selector switch may be worn/oxidized. Mercury, eh? Sounds like it's time for a new one anyway. Even if it doesn't solve the problem, it's still a good investment and riddance of a hazard.


Okay I changed the theromstat to an electronic one and checked the contections twice. But unfortunately the same problem exists. The furnace will come on then shut off before the desired tempurature is reached. If I manually turn off thermostat to the "off" position then back to the "on" position the furnace starts back up again, but still shuts off before the desired tempurature is reached.

Any help would be apprciated.

Danny

KC13
Feb 22, 2009, 06:26 PM
The new t-stat is still a good investment, sorry it didn't correct the problem. Switching the system off/on is cancelling a timed lockout imposed by the circuit board control. Since you have a condensing furnace and the problem seems more prevalent in colder weather, I would suggest checking the drain tubes and trap for blockage. Remove and flush thoroughly with water. Check the intake (if present) and exhaust pipes for blockage or horizontal sags which may be trapping water.

mygirlsdad77
Feb 22, 2009, 06:27 PM
Try cleaning the flame senser. Simple to do and doesn't cost you a thing. The flame senser will have one wire going to it, it will have one screw that holds it in place. It will be on the opposite side of the burner from the ingniter. Just remove it, clean it with an abbrasive cloth(sandpaper, sandcloth, steelwool, etc). Don't confuse it with the igniter. The flame senser will be a single probe. Please clean it and let us know if the furnace works. If it doesn't work after doing this, then we will take the next step.

twilley
Feb 22, 2009, 07:11 PM
try cleaning the flame senser. Simple to do and doesnt cost you a thing. The flame senser will have one wire going to it, it will have one screw that holds it in place. It will be on the opposite side of the burner from the ingniter. Just remove it, clean it with an abbrasive cloth(sandpaper, sandcloth, steelwool, etc). Dont confuse it with the igniter. the flame senser will be a single probe. Please clean it and let us know if the furnace works. If it doesnt work after doing this, then we will take the next step.


I have search the internet for pictures of where the flame seņor might be on the furnace but I have not had any luck. I also looked at my furnace with no luck. I tried to upload a picture of my furnace with no luck. Thanks for your help.

Danny

KC13
Feb 22, 2009, 07:17 PM
Stay tuned, hvac1000 will eventually see this, post a pic of some flame sensors for you, and pad his retirement fund once again.:D

mygirlsdad77
Feb 22, 2009, 07:17 PM
Sorry Danny, I won't give out my email. Nothing personall, I just can't bring myself to do it. I suggest not giving yours out publicly either. If you want to give it out, maybe try sending it in a personal message.

I really do want to help you. If you could just give the make and model of your furnace, I should be able to look it up and locate flame senser. Good luck.

twilley
Feb 22, 2009, 07:26 PM
Sorry Danny, i wont give out my email. Nothing personall, i just can't bring myself to do it. I suggest not giving yours out publicly either. If you want to give it out, maybe try sending it in a personal message.

I really do want to help you. If you could just give the make and model of your furnace, i should be able to look it up and locate flame senser. Good luck.

No worries I completely understand. I really to appreciate your help. Here is the info you requested.

Brand of furnace- Ruud Deluxe 90 Plus
Exact model number of furnace- UGED-06EMAES

KC13
Feb 22, 2009, 07:29 PM
Sorry Danny, i wont give out my email.I'll sell it to you... or accept hush money from MGD not to... :D

hvac1000
Feb 22, 2009, 08:09 PM
OK Danny lets try a cheap and quick test. Disconnect the R and W wires at the terminals at the furnace. Then jump the R and W terminals with a piece of wire or jumper cord. Turn the furnace back on and let it run. It should continue to run non stop. The temperature will continue to rise in the home but no harm will be done. Stay by the furnace and watch it operate and note any deviation from the constant burner running. After 10-15 minutes of this turn the unit off and report back with exactly what happened.

hvac1000
Feb 22, 2009, 08:12 PM
Here is the flame sensor as requested$$$$$

twilley
Feb 22, 2009, 08:28 PM
OK Danny lets try a cheap and quick test. Disconnect the R and W wires at the terminals at the furnace. Then jump the R and W terminals with a piece of wire or jumper cord. Turn the furnace back on and let it run. It should continue to run non stop. The temperature will continue to rise in the home but no harm will be done. Stay by the furnace and watch it operate and note any deviation from the constant burner running. After 10-15 minutes of this turn the unit off and report back with exactly what happened.

I will do it right now. I will get back to you in a few. I feel like I am in the middle of an inside joke with the flame sensor picture (mentioned by KC13) and $$$$$.

Thanks for your help.

hvac1000
Feb 22, 2009, 08:37 PM
I feel like I am in the middle of an inside joke with the flame sensor picture (mentioned by KC13) and $$$$$.

You are but do not tell anybody. LOL

twilley
Feb 22, 2009, 08:47 PM
[F Danny lets try a cheap and quick test. Disconnect the R and W wires at the terminals at the furnace. Then jump the R and W terminals with a piece of wire or jumper cord. Turn the furnace back on and let it run. It should continue to run non stop. The temperature will continue to rise in the home but no harm will be done. Stay by the furnace and watch it operate and note any deviation from the constant burner running. After 10-15 minutes of this turn the unit off and report back with exactly what happened.


I recognize that I am not the most keen person around but I cannot find the flame seņor. I found the ignitor but not the seņor. But I did jump the R & W terminals and the furnace came on. The furnace would light up but only for a minute or so, then cut off. The blower would continue to run. The furnace tried to light 3 times then shut off completely.

I hope I explained everything clearly enough.

hvac1000
Feb 22, 2009, 09:34 PM
There is a flame sensor somewhere. The book calls for

Microamps of flame circuit (1.0 minimum, up to 7.0 better)
Also check continuity of the ground wire.

Rheem Rudd same basic furnace with name change has had problems with this unit of yours. Last report they were offering 375.00 towards a new furnace but if it is on LP gas and not Natural gas the furnace can be had for free with the right arm twisting. That you would have to take up with a local Rudd distributer.

I believe your unit might also be the drum design and that unit was just plain bad news. Can you post some pictures of the burner area? If so I can probably locate the flame sensor if so equipped.

KC13
Feb 23, 2009, 04:37 AM
If it's the Imperial Drum design, there is no OEM remote sensor. The ignitor does double-duty on this one, unless an add-on remote sensor has been installed (look for a wire tap on the harness to the ignitor). Imperial... yeah, right.:rolleyes:

KC13
Feb 23, 2009, 04:50 AM
I feel like I am in the middle of an inside joke with the flame sensor picture (mentioned by KC13) and $$$$$.You are. Keep still, my aim isn't what it used to be.:p

hvac1000
Feb 23, 2009, 09:30 AM
There were two reasons to ask about the drum. The sensor since he could not find one and the cracks in the drum for 375.00 I believe. If he has no sensor and if the furnace was not changed over to the new style ignitor/modual system by now it is probably best to replace that POS.

KC13
Feb 23, 2009, 03:25 PM
POS is putting it nicely. There's nothing "Imperial" about those drums. "Inferior Drum" would be more appropriate.;)

twilley
Feb 23, 2009, 03:52 PM
There were two reasons to ask about the drum. The sensor since he could not find one and the cracks in the drum for 375.00 I believe. If he has no sensor and if the furnace was not changed over to the new style ignitor/modual system by now it is probably best to replace that POS.

Okay,
After a cold night of sleeping I woke up this morning and examined the furnace some more. The furnace goes through 5 cycles of lighting then shutting down completely (I realized that late last night). A guide on the control panel door said that it could be one of two problems. The first being the control board needs to be replaced. So I took the screws off the control panel doors and low and behold in the upper left corner of the control board there was a brown/burn mark that appears to be a fried portion of the control board.

So I am thinking that I need a new control board/panel.

Danny

KC13
Feb 23, 2009, 03:57 PM
So I am thinking that I need a new control board/panel.

DannyThe new furnace comes with one.;)

mygirlsdad77
Feb 23, 2009, 05:37 PM
Need to know if this is indeed an imperial. If so, replace furnace. How old is furnace, they haven't made imperials for quite a few years. It may be time to call in a tech to assess the furnace. The board definitely sounds like a problem, but I hesitate to tell you to replace board when there may be other issues with the furnace. Could become a money pit(especially if its an imperial). Please let us know what you decide.

Ps, the new rheem/ruud furnaces are much better. Don't be scared of them for past mistakes. All furnaces have had their bad years of manufacture. If you decide to replace, just gets at least three different quotes from reliable contractors. Hope all works out for you.

KC13
Feb 23, 2009, 05:44 PM
F.Y.I. I checked on a replacement h/x drum in November and was told they are no longer available. For the few that are still in warranty, the manufacturer is offering a minimal credit toward a replacement unit (must be same brand).

twilley
Feb 23, 2009, 06:07 PM
Need to know if this is indeed an imperial. If so, replace furnace. How old is furnace, they havent made imperials for quite a few years. It may be time to call in a tech to assess the furnace. The board definately sounds like a problem, but i hesitate to tell you to replace board when there may be other issues with the furnace. Could become a money pit(especially if its an imperial). Please let us know what you decide.

ps, the new rheem/ruud furnaces are much better. Dont be scared of them for past mistakes. All furnaces have had their bad years of manufacture. If you decide to replace, just gets at least three different quotes from reliable contractors. Hope all works out for you.

How can I tell if it is an imperial?

hvac1000
Feb 23, 2009, 06:09 PM
Can you post some pictures?

KC13
Feb 23, 2009, 06:35 PM
How can I tell if it is an imperial?Does the center area of the furnace resemble a large, round, bolted horizontal bulkhead?