My limit switch come on then go off over and over.

KC13
Jan 11, 2009, 08:53 AM
The unit is probably overheating. Start by checking the air filter.

jordan1977
Jan 11, 2009, 09:00 AM
The unit is probably overheating. Start by checking the air filter.

I already check the filter its clean and the vent stack is clear of debris

KC13
Jan 11, 2009, 09:09 AM
Does the blower run?

jordan1977
Jan 11, 2009, 09:23 AM
Yes the blower run good

KC13
Jan 11, 2009, 09:28 AM
Is anything blocking or restricting the supply and/or return registers?

jordan1977
Jan 11, 2009, 09:40 AM
No the return is close to the ceiling. Can the coil be restricting enough to over heat the unit. I did not check that or could just be the limit switch.

KC13
Jan 11, 2009, 09:47 AM
An airflow restriction of some type is more likely. If the indoor coil is clogged with dirt, your air filtration is probably insufficient.

hvac1000
Jan 11, 2009, 10:09 AM
It could also be a weak or out of range limit switch if all else checks out. You might also check the gas pressure and make sure it is as listed on the furnace label. A furnace that is overfired can also cause this problem.

jordan1977
Jan 11, 2009, 10:28 AM
Thank you I will check the coil if that check out I will check the gas pressure. I just want to be sure before I get a new limit switch and have the same problem

hvac1000
Jan 11, 2009, 01:25 PM
Smart move. Many folks just run out and buy a part and think the problem is solved and that in many cases is not the way it works.