I had about the same problem last heating season. One repairman said it needed a new control board and then online I read about the pilot ignitor. I replaced stark electrode and pilot burner and it seemed to fix it. The it started again so since I bought the control board online previous, I put that in too. Well it worked perfect all last season and a few days this year. Then it started acting up again. It lights the pilot and main burner but then both of those go out after maybe 2 minutes (sometimes). Then it will rapidly sort of click off and on like it's trying to start up again all the while the main blower is still running (as it should since it just shut down). I smelled gas awhile ago, disconnected everything and aired out the furnace room. I came home hrs later and started it again only to see it fail as described. Then when I tried again in about 10 min it ran right up to target temperature (10mins) like nothing was wrong.

I don't trust it anymore so it's become a manual system until I can fix or replace it. I'm about to dump $$$ on a new York Pulse unit unless anyone has any sage advice for me. It's 21 yrs old now. Thanks

wmproop
Dec 22, 2008, 06:54 PM
York is OK,, if it `s installed correctly

sdcruiser
Dec 26, 2008, 11:09 AM
I've got the symptoms down a little better now. Cold morning, 45 outside and 63 inside, heat off at thermostate. Turn heat on and furnace begins start cycle and warms for about 2 min. Then flame goes out and furnace runs cool down cycle with main fan running (has not hit target of 67 yet) then it once again initiates a light off and warms the house to the target temperature just fine. The next time it tries to warm it may work fine or it may cycle while it tries to light off the ignitor. I usually shut it off manually because I have smelled gas at this point. It has a new 3 wire ignitor assy and the main control board assy replaced last winter. Any thoughts on what I might replace while freezing in san diego (OK not really that bad) waiting for the quotes to come in. How about the temperature sensor right above the main burners? Thanks

KC13
Dec 27, 2008, 08:13 AM
Considering the action you describe and the parts you have replaced already, it sounds like you have a faulty pressure switch. The unit will attempt to establish pilot, but the absence of the pressure switch circuit is not powering the holding coil of the gas control. The pickup coil is dropping out when the pilot switches to the hot contacts. Since you haven't posted the model number, this would only be true if your furnace is an induced-draft design.

sdcruiser
Dec 27, 2008, 10:54 AM
It's the 58ss080CC. Yes it does have an air pressure sensing switch, large round device with the sensing line.

Funny thing is the first repair man said it was the board but then I put the ignitor in first and that "seemed" to fix it. But I had the board and when it acted up again I put that in because I could not get my money back. It operated fine all last season. But one estimator thought that it wasn't the board or ignitor but pointed out something in the draft induction system.

Looks like furnaceparts is out of this part. Is there anyway to jumper around this to check if it is the problem? There are 3 wires to it. One is NO (normally open), NC (normally closed) and C for common I think. It's a $90 part. If there's no way to jumper maybe I can "borrow" one from a neighbor. We all have the same 21 yr old Carrier.

Thanks for the advice. I see flashes from the board under the pressure switch when it starts cycling. I took all the board out today, cleaned contacts, inspected for missing solder, etc. It did the same thing and I can hear the valve opening and then closing maybe 30 secs later... when it senses no pressure generated I bet!

KC13
Dec 27, 2008, 11:13 AM
If poor or compromised draft conditions aren't a factor, it is likely that the switch contacts are oxidized, presenting an inconsistent problem that can be difficult to pinpoint. A voltmeter connected between NO and C would reveal if the switch circuit is breaking when the problem occurs.

sdcruiser
Dec 27, 2008, 11:30 AM
Your hunch was correct. I think the NC portion of the switch needs to stay that way to enable start up, the NO portion must close to keep the valve open. The NO of my switch is operating fine but the NC opens with pressure and causes the valve to close. So I jumpered it as it started so that both are NC and the furnace is running now. I need to confirm the flue is not plugged and I'm not bypassing this because of another problem. Does this sound right? It's now above 59 in the house thanks to you.

sdcruiser
Dec 27, 2008, 12:24 PM
Leave it to an Ohioan to help a former Ohioian. I'm in San Diego now. I found the part online for $71 and I'm looking in San Diego now. I checked the flue on the roof and no obstructions. The small fan is working but not sure about the larger one that makes the draft. Since the normally open portion of the switch does close I'm wondering if this means the inducer is making pressure? The NC portion opens causing the valve to close. I need to find a theory of operation somewhere I think. Thanks again.

KC13
Dec 27, 2008, 12:34 PM
If you jumpered NO to C and the unit sustains operation, that proves the switch was not maintaining the circuit. Make sure the switch circuit isn't breaking due to a problem with the combustion draft. The "flash" from the board? Likely the inducer relay arcing. If inducer operation becomes erratic this may be why.

KC13
Dec 27, 2008, 12:38 PM
Leave it to an Ohioan to help a former Ohioian. I'm in San Diego now. I found the part online for $71 and I'm looking in San Diego now. I checked the flue on the roof and no obstructions. The small fan is working but not sure about the larger one that makes the draft. Since the normally open portion of the switch does close I'm wondering if this means the inducer is making pressure? The NC portion opens causing the valve to close. I need to find a theory of operation somewhere I think. Thanks again.What a coincidence... my oldest son lives in S.D. serves in the navy, stationed at Coronado.

sdcruiser
Dec 27, 2008, 01:00 PM
Small world. I've been here since 1971 and grew up in Cleveland.

I pulled the draw motor assy just to check. Everything seems normal for a 21 yr old carrier. I sealed it back up with hi temp rtv and I'm going to order the pressure sensor now. So can I send you some coffee. I roast as a side business and hobby and would like to pay you back for your willingness to share your knowledge. You saved me about $9K this year. I know one of these years I'll have to replace this thing along with the AC but not this year at least. Thanks again.

KC13
Dec 27, 2008, 01:11 PM
Small world. I've been here since 1971 and grew up in Cleveland.

I pulled the draw motor assy just to check. Everything seems normal for a 21 yr old carrier. I sealed it back up with hi temp rtv and I'm going to order the pressure sensor now. So can I send you some coffee. I roast as a side business and hobby and would like to pay you back for your willingness to share your knowledge. You saved me about $9K this year. I know one of these years I'll have to replace this thing along with the AC but not this year at least. Thanks again.Sweet! I'd love some! Check your private messages.

sdcruiser
Dec 31, 2008, 04:03 PM
So the pressure sensor arrived today and I installed it. Plugged the unit back in and fired it up. Up until now I've been jumpering both contacts closed and it's been operating perfectly.

So the pilot lit, mains lit, it heated for about 2 min and then when I came back in from outside the pilot was again on and it was going through another start cycle which it did and it ran for many minutes just fine. I'm going to try it again but in the middle of the cycling I think it did THIS a time or two also. So I may be chasing two problems. I'm probably going to put something in this summer.

I got the quote for the Goodman 2 stage variable 95% and 16 seer AC along with duct cleaning and it's about $8K. I think the installer didn't want to believe my heat load calcs (I did several) and upsized the furnace and AC (4 ton instead of 3 ton). It may be because the smaller unit might not have enough air flow @ 1200 cfm for a 2100 sq ft 2-story house I suspect.

Oh the coffee was shipped out today. I don't think the Kona is that great but the Nicaragua is very good.

sdcruiser
Dec 31, 2008, 06:08 PM
I just tested it again and this time it started and ran for about 4.5 min at which time the pilot and main went out and system started cycling again, clicking on off on off.

So I jumpered it again, NO to NC and NC to NC and it started and ran just fine. I even jumpered the NC to NO while it was running and it ran fine and did not quit.

So I checked the switch while it was running and the NC goes to NO when burners are lit and the NO goes to NC. I didn't see it change until the burner shut off when it reached the set point. I'm not sure what the state is when it's cycling but the switch seems to be behaving as expected. I wish I knew what the NC and NO switch purposes were so I could trouble shoot this better. Looks like there's a new furnace in my future after all unless I can get this figured out soon.

KC13
Dec 31, 2008, 11:56 PM
NO is normally open, NC is normally closed, and C is common. At rest, C connects to NC, and NO is isolated. When running, C connects to NO, and NC is isolated. If possible, connect a voltmeter across C and NO, and observe meter when drop-out occurs. Unless switch is disengaging, you should read 0 volts.

MarkwithaK
Jan 1, 2009, 02:01 AM
I got the quote for the Goodman 2 stage variable 95% and 16 seer AC along with duct cleaning and it's about $8K. I think the installer didn't want to believe my heat load calcs (I did several) and upsized the furnace and AC (4 ton instead of 3 ton). It may be because the smaller unit might not have enough air flow @ 1200 cfm for a 2100 sq ft 2-story house I suspect.

As usual I have to say that I would steer clear of the variable speed motors. As far as oversizing your A/C, you have to be very careful about how you size the capacity. Most people do not realize that one thing the A/C system does is remove humidity from your house along with heat. On an over-sized system the heat will be removed but the humidity will not. This can cause problems ranging from an uncomfortable humidity level on up to mold issues cased by the humidity. Likewise, an over-sized furnace can have problems with the high limit if your duct work is not the correct size/configuration. Keep in mind that an improperly sized system could void any warranty.

sdcruiser
Jan 1, 2009, 09:41 AM
As usual I have to say that I would steer clear of the variable speed motors. As far as oversizing your A/C, you have to be very careful about how you size the capacity. Most people do not realize that one thing the A/C system does is remove humidity from your house along with heat. On an over-sized system the heat will be removed but the humidity will not. This can cause problems ranging from an uncomfortable humidity level on up to mold issues cased by the humidity. Likewise, an over-sized furnace can have problems with the high limit if your duct work is not the correct size/configuration. Keep in mind that an improperly sized system could void any warranty.

Yes that's my concern too with the 4 ton single stage system. The existing 10 seer 4 ton doesn't run all that long, however our humidity in San Diego isn't all that bad either. With a two stage AC (not offered in a Goodman until 5 ton) you have some flexibility. Two story houses of course really suffer without zoning because the upstairs is generally too warm on those few hot days where you need AC. So that's one reason all vendors here seem to ignore calcs and go with the rule of thumb. Even my worst case 40 deg day and 70 inside that yields about 28 K Btu/hr is ignored. I've checked it 3 ways including timing run time of the existing 72K Btu/Hr net unit and have come up with less than 30K every time. But they still want to install a 70-80K furnace.

Oh and the ducts are a nightmare with high noisey velocities on the two close downstairs ducts and only the one cold air return in the family room. The first register is only about 10 feet from the furnace and I've put a blue coarse filter in back of the register to quite it down. I won't go into how the cold air return was in the beginning but they utilized a false ceiling and hollow walls. When that didn't meet code they tried to put the cold air return right above the dryer in the wash room. The family room location was a compromise and I've added some baffling in the cold air return to quiet it down some. You can look into the cold air return and see the bottom of the furnace otherwise!

So I have heard the original variable motors had problems but that the latest generation has solved those issues that over-stressed many motors. Any truth to this?

KC, so far I've just looked at what the switch is doing statically. The resistanceof the NO portion when closed and furnace jumpered to run does creep from .05 K ohm to about .15 k ohm due to the temperature change but I don't see anything else unusual. Yet it works perfectly if I just jumper the wires as if everything is NC. For safety I disconnect the NO open leads once the furnace completes a cycle. I'm not sure if this is necessary and I'm too safety minded to run the furnace jumpered when I'm not at home. I'm sure I'm compensating for some other issue. I thought for sure the pressure switch would fix it. When it ran for 4.5 min perfectly I thought it was going to be OK but something caused it to "blow out" and then start cycling as if it was trying to re-start.

MarkwithaK
Jan 1, 2009, 10:22 AM
What calculations are you working off? Have you done a Manual J on the building?



So I have heard the original variable motors had problems but that the latest generation has solved those issues that over-stressed many motors. Any truth to this?

I have said this numerous times in other threads and let me repeat myself before those that praise the VS motor jump my back, my issue with variable speed motors is not their quality but their high repair/replace costs. Based upon rates in my area and my cost I can replace an entire system (high efficiency w/ conventional blower, 15 SEER condenser and Evap coil) for the same it would cost to replace a VS motor when you factor in labor and mark-up.

sdcruiser
Jan 1, 2009, 10:33 AM
Yes I can imagine the variables are costly. But if they last as long as a conventional is that really an issue? My conventional motor is 21 yrs old now. Is your experience that the variable need to be replaced more often. I'm sure the usage in your area is higher too.

MarkwithaK
Jan 1, 2009, 10:41 AM
Do not expect 21 years out of either a VS motor or a conventional motor for that fact. Quality just isn't the same. Newer parts are designed to eventually fail, that's just the harsh reality. Just to throw some numbers at you, to replace a VS motor you're looking at between $1000.00- $1200.00 easy and that is just for the motor. Factor in labor and you could up around $1400.00 If your local service company's mark-up is higher then obviously your total bill will also be higher.

sdcruiser
Jan 1, 2009, 10:42 AM
OK, I just had a thought. I have not been paying attention to what the draft motor is doing. Maybe it's the source of all of this, dahhh. If the draft motor slows or gets intermittent it would cause the switch to misbehave. Bypassing the switch resolves this but the motor is probably still going to run erratically if it's the problem. I'll check next time I run the furnace.

KC13
Jan 1, 2009, 11:35 AM
If you jumpered NO to C and the unit sustains operation, that proves the switch was not maintaining the circuit. Make sure the switch circuit isn't breaking due to a problem with the combustion draft. The "flash" from the board? Likely the inducer relay arcing. If inducer operation becomes erratic this may be why.I had a feeling about this earlier, but you hadn't indicated that the motor was "sputtering". You had taken out the board that is housed behind the pressure switch before. The inducer motor relay is on this board, enclosed by a cubic-shaped cover. If you look closely and proceed carefully, you can remove this cover with a small screwdriver wedged under the tabs on the relay. I'd be willing to bet you will find the relay contacts burned. Carefully clean them with abrasive cloth and see if the motor runs more consistently. If so, the board should be replaced as a "permanent" solution. When you re-install the board, pay attention to the mounting tabs engaging into the housing properly. Afterward, give us a full report!

KC13
Jan 1, 2009, 11:47 AM
I had a feeling about this earlier, but you hadn't indicated that the motor was "sputtering". You had taken out the board that is housed behind the pressure switch before. The inducer motor relay is on this board, enclosed by a cubic-shaped cover. If you look closely and proceed carefully, you can remove this cover with a small screwdriver wedged under the tabs on the relay. I'd be willing to bet you will find the relay contacts burned. Carefully clean them with abrasive cloth and see if the motor runs more consistently. If so, the board should be replaced as a "permanent" solution. When you re-install the board, pay attention to the mounting tabs engaging into the housing properly. Good luck, afterward, give us a full report!For some reason this didn't post as most recent.

sdcruiser
Jan 1, 2009, 12:09 PM
So I watched it run and the inductor fan ran smoothly. I also monitored the NO closed conncection and it remained NC. Pinching the silicone sensing line worked as expected, NC went to NO and NO went to NO on the meter.

I did have that board off but didn't realize the cover came off the relay. I'll pop it off and inspect. That is where I saw all the flashing when it cycles and just that might have damaged the contacts. I hope the motor is OK because it's not available and the replacement is expensive. I'll go check the contacts. I think I have a points file and contact cleaner.

KC13
Jan 1, 2009, 12:17 PM
Easy on the file! Don't wear off the contacts to the point that they don't meet firmly. I would prefer if you used some fine abrasive cloth. Cut a narrow strip and gently clean off contacts. This is not a typical service procedure but can get a unit running until the board can be replaced.

sdcruiser
Jan 1, 2009, 12:50 PM
Guess I won't cancel the coffee shipment, lol. Boy those contacts are tiny. One side was blackened with lots of soot inside the cover. I used some fine 600 grit paper and contact cleaner and it fired right up. It's too warm for anymore testing so I'll give it go again tonight. Thanks again.

KC13
Jan 1, 2009, 01:03 PM
I feel confident that we have pinpointed the source of your problem, once and for all. If you end up replacing the board, the new one will likely come in a kit with some wires to add on. Follow the instructions and you'll do just fine. For someone who's not a "furnace man", you have done quite well with this. I'm so... (sniffle)... proud of you!:p

KC13
Jan 1, 2009, 01:13 PM
Let me repeat myself before those that praise the VS motor jump my back. Too late! We heard that and we're comin' for you!:D

MarkwithaK
Jan 1, 2009, 01:18 PM
Too late! We heard that and we're comin' for you!:D
I have a catapult and a large stockpile of old dead motors... you'll never breach the perimeter.:)

sdcruiser
Jan 1, 2009, 01:27 PM
I feel confident that we have pinpointed the source of your problem, once and for all. If you end up replacing the board, the new one will likely come in a kit with some wires to add on. Follow the instructions and you'll do just fine. For someone who's not a "furnace man", you have done quite well with this. I'm so... (sniffle)...proud of you!:p

It just goes to show you that you even teach old engineers new tricks. And I didn't even blow up anything. I used to be a motorcycle mechanic years ago and I'm pretty used to working on things. I guess that's why I became a mechanical engineer. I found the board on eBay for about $98 and it's in City of Industry, CA. So I'll run it for awhile just to make sure. I see the new one has lots of extra circuitry like caps, probably to better protect the relay.

Given the age of this furnace, I'm concerned about some small flames I see coming out the sides of the burners when running. It's not a jet or anything but sort of a gently small candle size flame where the seams meet. The heat exchanger itself is in good shape. I'm sure there will be lots of good deals and rebates this year so if it lasts through our very mild heating season I might just replace it soon anyway.

MarkwithaK
Jan 1, 2009, 01:29 PM
Are the burners a long sword like design? Depending on where the flames are popping out they could be deteriorated.

sdcruiser
Jan 1, 2009, 01:36 PM
Are the burners a long sword like design? Depending on where the flames are popping out they could be deteriorated.

They're more like small horns, maybe 4-5 inches long, three of them. They look like a two piece design with the two halves split horizontally. That where the small "leaks" are and right at the end only where the flames exit.

KC13
Jan 1, 2009, 01:40 PM
[QUOTE=sdcruiser;1457578 Given the age of this furnace, I'm concerned about some small flames I see coming out the sides of the burners when running. It's not a jet or anything but sort of a gently small candle size flame where the seams meet. [/QUOTE] The crosslighters may be spread open a little wider than normal due to the age of the unit. They can be crimped down a little to reduce this condition, but don't overdo it or late ignition may result due to poor flame carry-over. Use a dime as a gauge.

MarkwithaK
Jan 1, 2009, 01:44 PM
I have yet to see a 21 year old system with in-shot burners. That's a new one on me.

sdcruiser
Jan 1, 2009, 02:11 PM
I have yet to see a 21 year old system with in-shot burners. That's a new one on me.

Not sure what in-shot means but I attached a pic. It's the first of the carrier 82% AFUE furnaces and the house was built in 1987. I'm the original owner.

hvac1000
Jan 1, 2009, 02:28 PM
One of the original Carriers and it is still running. Does it have the three wire pilot. If so that can give you a fit sometimes. They will allow the unit to run then drop out of the circuit at any time. The link is for some of the original specs on that unit.


http://www.xpedio.carrier.com/idc/groups/public/documents/techlit/58ss-1p.pdf

sdcruiser
Jan 1, 2009, 02:49 PM
One of the original Carriers and it is still running. Does it have the three wire pilot. If so that can give you a fit sometimes. They will allow the unit to run then drop out of the circuit at any time. the link is for some of the original specs on that unit.


http://www.xpedio.carrier.com/idc/groups/public/documents/techlit/58ss-1p.pdf


Yes it has the 3-wire. I replaced it last season. At that time I bought the main control board because a tech that came out said that was the problem. It ran for awhile with just the ignitor assy replaced and so I did put the board in and it seemed OK all last year and some of this year. Then it started some similar behavior this year. Looks like the relay contacts in the inducer board were messed up because cleaning them has seemed to make the problem go away, at least in the last 3 starts today.

hvac1000
Jan 1, 2009, 02:56 PM
Yes I read where you had replaced the three wire pilot. Just because it is almost new does not mean it is working correctly was the point I was trying to make. Over the years I have had them fail with in a week of replacement so I was just mentioning the fact of not taking that off the list of possibilitys. They are adjustable but that is something best left to the pro's since it is a safety device.

Back in the day we sold many of those SS models of Carrier. For the time they were a good unit except if you got some of the originals with the cold rolled steel heat exchanger. They rusted out quick but they were replaced with aluminized steel and those lasted longer.

sdcruiser
Jan 1, 2009, 03:06 PM
Yes I read where you had replaced the three wire pilot. Just because it is almost new does not mean it is working correctly was the point I was trying to make. Over the years I have had them fail with in a week of replacement so I was just mentioning the fact of not taking that off the list of possibilitys. They are adjustable but that is something best left to the pro's since it is a safety device.

Back in the day we sold many of those SS models of Carrier. For the time they were a good unit except if you got some of the originals with the cold rolled steel heat exchanger. They rusted out quick but they were replaced with aluminized steel and those lasted longer.

Yes I heard that about this unit from the Lennox dealer here. He originally installed a lot of carriers and remarked that my HX looked good. Yes I suspected the ignitor too. I noticed that the gap can be set but I didn't see any other adjustment on it. It has a fixed orifice. That seems to be working and lighting off correctly so let's hope that's not it. There are about 100 of these carriers in my development. I wonder if any have had this many problems. It was trouble free for about 20 yrs so I can't really complain.

hvac1000
Jan 1, 2009, 03:27 PM
Do not expect to get 20 years of trouble free service out of any of the new ones since that will never happen. I guarantee you will be spending some big $$$ if you buy a variable speed blower on any unit after the warranty is over. While the DC conversion has merit the true long range cost/energy savings are bogus.

sdcruiser
Jan 1, 2009, 03:58 PM
Do not expect to get 20 years of trouble free service out of any of the new ones since that will never happen. I guarantee you will be spending some big $$$ if you buy a variable speed blower on any unit after the warrenty is over. While the DC conversion has merit the true long range cost/energy savings are bogus.

Yes, I'm reading another thread here about 2-stage vs modulating and my head is spinning. I might just do what it takes to keep this 82% carrier running for awhile lol. So does that slight "leak" at the sides of my burners look like a problem in the pic. I guess I could try squeezing the sheet metal together there slightly to see if I can reduce it.

hvac1000
Jan 1, 2009, 05:17 PM
The burners have a built in flame jumper circuit to allow the pilot to lite off the closest burner then the flame travels to the other burners to lite them off from there. The side burn you are talking about does not look to severe. If you choose to try and close them down it might cause more problems than leaving them alone. Keep your eyes on Ebay. Every once in a while someone puts a new set up for auction and they go cheap. I know I do not have any in my personal stock in my old warehouse in the industrial park from years ago. Most of the stuff left there is for ammonia refrigeration and come to think of it I should probably unload that stuff and give my tenant the rest of the cage space. That stuff has been sitting there for 15 years. LOL

If you try to crimp them down easy does it since the metal is old and well tempered if you know what I mean.

KC13
Jan 1, 2009, 05:51 PM
The unit in the pic looks pretty good for 21 years old. Must be the mild winters and not being exposed to road salt.:p

mygirlsdad77
Jan 1, 2009, 05:52 PM
Goodman two stage is an awesome furnace. One of, if not thee highest effiency ratings, and lower priced than most competitors. Not at all problem matic(as long as installed correctly). Doesn't have the variable draft inducer. You could almost buy one of these goodmans for the price of one variable motor.

hvac1000
Jan 1, 2009, 05:54 PM
Yes but the Goodman has one of those funny all in one gas valves that do not work unless you play with the wires. LOL

mygirlsdad77
Jan 1, 2009, 05:57 PM
Only been doing goodmans for about four years, but haven't had one single problem with gas valve or wiring.

KC13
Jan 1, 2009, 06:09 PM
The truth is hidden in the name. Go to wordsmith.org, click on "internet anagram server", type in goodman, click on "get anagrams". Pretty funny stuff. "Evander Holyfield" gets you "lived holy 'n' fed ear". Brett Favre? "Beer fart TV". :D

mygirlsdad77
Jan 1, 2009, 06:20 PM
Is that kind of like saying :you buy a rheem, your going to get reemed. I got a payne and oh what a pain it is. Can't stop a train, its just getting it to start that's hard. Carrier. Im sick of hauling this thing around. Lennox, well, lets just say it sounds like a drug that should come with the unit to keep you from going crazy.
Goodman. Yep, you're a Good Man for having the sense to buy me.

sdcruiser
Jan 1, 2009, 06:26 PM
The unit in the pic looks pretty good for 21 years old. Must be the mild winters and not being exposed to road salt.:p

Yeah I hated when my dad made me knock the slush off our furnace in Cleveland!

Oh I ran it another two times with no issues. Thanks

KC13
Jan 1, 2009, 06:31 PM
It's more like, "O G O D A M N".

mygirlsdad77
Jan 1, 2009, 06:37 PM
As in O GOD DAMN this is an awesome furnace?

KC13
Jan 1, 2009, 06:40 PM
As they say, "beauty is in the eye of the beerholder"... maybe we should do the wordsmith to some other brands...

hvac1000
Jan 1, 2009, 06:40 PM
Actually the Goodmans we have tested over the years have all been OK with the exception of the heat X rings that would pop a few years ago. The most important factor with any equiptment is the quality of the install. You can take the most expensive equipment and turn it to junk with a bad install.

mygirlsdad77
Jan 1, 2009, 06:46 PM
Exactly right hvac. All new furnaces are pretty much the same(some do tend to overkill in design with no noticeable increase in function, just makes them harder to trouble shoot.) Install is key.

KC13
Jan 1, 2009, 06:54 PM
Okay, "Lennox heat" can also be "hotel annex", as in you might end up in one when it breaks down. Or, "He lent an ox", to haul it away, I imagine...

mygirlsdad77
Jan 1, 2009, 07:07 PM
Yep Lennox sucks.LOL

MarkwithaK
Jan 1, 2009, 07:16 PM
Is that flexible gas line legal in your area? In Indiana it is a no-no.



Can't stop a train, its just getting it to start thats hard. Now that's funny!

sdcruiser
Jan 1, 2009, 07:37 PM
Is that flexible gas line legal in your area? In Indiana it is a no-no.


Now that's funny!

Yes they even use it on the water heater.

MarkwithaK
Jan 1, 2009, 07:40 PM
It is legal to use it on water heaters here but illegal to use in any situation where the line would pass through the cabinet, such as a furnace.

KC13
Jan 1, 2009, 07:41 PM
Indiana won't allow it due to all of the earthquakes... which... never happen in SoCal...

MarkwithaK
Jan 1, 2009, 07:41 PM
In addition, you cannot have a union inside the cabinet here. A furnace must be hard piped from gas valve on back lol.

MarkwithaK
Jan 1, 2009, 07:43 PM
Indiana won't allow it due to all of the earthquakes...which...never happen in SoCal...

Yeah because Indiana gets soooo many... ya goon! Lol

We did get one back when I was young. Lasted all of 10 seconds lol.

KC13
Jan 1, 2009, 09:18 PM
Here we go... "Trane furnace"... or "errant fan cue"... or "enact rear fun"... or "rent-a-furnace".

MarkwithaK
Jan 1, 2009, 09:49 PM
"enact rear fun"

I used to date this girl back in the day and well you know :p

KC13
Jan 1, 2009, 09:53 PM
I prefer microwave ovens, they don't brown your meat...

MarkwithaK
Jan 1, 2009, 10:00 PM
That's just wrong... funny... but so so wrong.

KC13
Jan 1, 2009, 10:41 PM
That's just wrong....funny....but so so wrong.Look man, I tried to warn you about my sister, but you wouldn't listen... "her mouth is so pretty..." I think I've hit rock bottom now, somebody please take this shovel from me.

hvac1000
Jan 1, 2009, 10:50 PM
Her name is not Vacuum Sally by any chance?

MarkwithaK
Jan 2, 2009, 05:50 PM
You know Sally??

hvac1000
Jan 2, 2009, 06:13 PM
Dang she told me I was the only one. LOL

KC13
Jan 2, 2009, 09:06 PM
Dang she told me I was the only one. LOLShe lied to everyone like that. Even her own father...

hvac1000
Jan 2, 2009, 09:11 PM
Thank god since it was my uncles child. LOL

KC13
Jan 2, 2009, 09:15 PM
She's married now. Met her cousband at a family reunion. Uncle daddy was so jealous...

hvac1000
Jan 2, 2009, 09:26 PM
According to his wife/girlfriend his plumbing is out of order so he could not do her any good no more anyway. PS that is why his wife/girlfriend see me now.. he does not look to good anymore either. I am thankful for being adopted.

KC13
Jan 2, 2009, 09:31 PM
Looks like a BMV photo. That's not his good side.

KC13
Jan 7, 2009, 07:39 PM
The truth is hidden in the name. Go to wordsmith.org, click on "internet anagram server", type in goodman, click on "get anagrams". Pretty funny stuff. "Evander Holyfield" gets you "lived holy 'n' fed ear". Brett Favre? "Beer fart TV". :D
Do you see "Rheem furnace"? Or, "fun cream here"? Or, "fear, hence rum"? Yes, I'm bored...

mygirlsdad77
Jan 7, 2009, 07:48 PM
Can you give me the one for ARTIC AIR.

KC13
Jan 7, 2009, 07:50 PM
Ask me help desk? Or, "desk leaks hemp"?

KC13
Jan 7, 2009, 07:56 PM
can you give me the one for ARTIC AIR.Not much, really. "I, circa tar". Pretty old, I suppose...

mygirlsdad77
Jan 7, 2009, 08:00 PM
Ask me help desk? Or, "desk leaks hemp"?

Wow, I would have really enjoyed this site about ten years ago. Ohhh, the good old days.

sdcruiser
Jan 7, 2009, 08:30 PM
Man I go away for few days and look where you've taken my thread. I don't suppose anyone is interested in if the inducer board I installed tonight fixed the problem? Naaaah, didn't think so.

KC did you get the coffee yet?

KC13
Jan 7, 2009, 08:39 PM
Yes indeed, and it's some good stuff! Thank you, and sorry for warping your thread. I don't know exactly where it all went wrong... :rolleyes:I was waiting for your feedback on the patient... how is she?

mygirlsdad77
Jan 7, 2009, 08:42 PM
Actually yes, we are very interested to know if your problem is solved. Sorry, we tend to chat a little much. We just like to have a little fun amongst ourselves while waiting for reply from poster. Please let us know if your problem is solved, and if not, then we will be here to try an help further. Once again, sorry about our personal back and forth on your page. Please don't let it affect your feelings on this site. This is a great site, and we are here to help. Take care,

Lee

sdcruiser
Jan 7, 2009, 08:52 PM
No I actually enjoyed it. Listening to gallows humor all day at work gets me wanting something different. So the patient appears to be cured. She fired right and worked perfectly. And it's a good think. The temp fix with the relay stopped working and I ended up wiring the swith to be NC all the time to get heat. I was a bit afraid to let it run like that unattended. The new board is only slightly differnent and needed some additional jumpers and wiring added to work. It was only $98 on eBay too.

So I'm not positive it also needed the pressure sensor assembly but those contact might have been bad too. Thanks for all the assistance and good humor.