View Full Version : Rheem Classic 90 starts burner - then stops.


superlars
Dec 14, 2008, 04:50 PM
I have a Rheem Classic 90 upflow heather. When it turns on the burner comes on fine but it stays on for just 5-10 seconds then shuts off. It does this twice then the blower comes on but with no flame going. The yellow flame sensor LED doesn't come on at any point. I have cleaned the flame sensor with steel wool. But apparently there is no power to the flame sensor. The two red LED's are on.
Any ideas?

KC13
Dec 14, 2008, 05:09 PM
Make sure you have a clean circuit to the sensor (not grounded), a solid ground to the burner assembly, and that all the burners are lighting.

MarkwithaK
Dec 14, 2008, 06:12 PM
Flame sensor could simply be shot.

superlars
Dec 14, 2008, 08:43 PM
Flame sensor could simply be shot.


It's $12 so why not try replacing it. It looks fine though. The furnace worked fine last winter. This was the first time to start it up this winter. But I guess no yellow light speaks to either a faulty sensor or a bad board.

hvacservicetech_07
Dec 14, 2008, 09:12 PM
Just replace it. I usually replace most flame sensors,unless I don't have one on the truck. You hate to have a call-back on a five dollar part. Check all of your connections.

Frank Mangrum
May 19, 2012, 09:57 AM
Just replace it. I usually replace most flame sensors,unless I don't have one on the truck. You hate to have a call-back on a five dollar part. Check all of your connections.Have you tried to check THE FLAME RECTIFICATION CIRCUIT?