PDA

View Full Version : Heater will not start a second time


rubeve03
Dec 6, 2008, 05:09 PM
I have a goodman model #pg8060100-1. when the heat is off for a while say a couple of hours the heat will come and shut off. But then it will not come back on I see the inducer fan working but nothing else could it be the switch that's connected to the inducer fan? Please help

mygirlsdad77
Dec 6, 2008, 05:20 PM
Check to make sure vent is not obstucted in any way. Check to make sure pressure switch is closing when draft inducer starts to run. You can take the two wires off pressure switch(switch connected to inducer) and jump them together after inducer starts to run.

hvac1000
Dec 6, 2008, 05:20 PM
Sorry no such model listed by Goodman

mygirlsdad77
Dec 6, 2008, 05:37 PM
Can you show your flame senser pic hvac, this may also be the problem.

hvac1000
Dec 6, 2008, 06:33 PM
can you show your flame senser pic hvac, this may also be the problem.