I have a Trane packaged unit model YCC036-SF-14A. It started not heating when heat was called for or just shutting off with out making set point. I thought is was the thermostat but with a new one same results. It will reset it I turn the thermostat off for 5 seconds then back on. I have no fault codes but the on the igniter board the LED stays on solid red when its in fault.
Would appreciate any advice you can give

KC13
Dec 6, 2008, 09:46 AM
Jumper the R-W circuit at the unit and see if the problem still occurs. If not, you have a problem with the thermostat or the wiring between the t-stat and the unit.

jsda
Dec 6, 2008, 02:20 PM
Does anybody have the fault codes for this furnace?

KC13
Dec 6, 2008, 02:29 PM
Fault code list/label can usually be found inside one of the service panels. In some cases it may be on the circuit board or ignition module housing.