generalts0
Dec 4, 2008, 08:20 AM
Hi all,
I'm installing a 30a 2-pole breaker in my breaker panel to be a dedicated line for a clothes dryer. The panel is Square D type QO with 100a main breaker and 20 breaker slots.
Clothes dryer manual says to use 10-3 cable, make sure to connect that 4th wire to the ground bar, or use 10-2 with a grounding strap and clamp that to a grounded object.
Home depot expert says the ground bar in the breaker panel is the metal bar with a cable bolted to it that terminates into the water main.
I used 10-3 and now have the black and red wires connected to the 2-pole breaker, and the white wire connected to the neutral bar where all the other white wires in there are connected.
The skinny, uninsulated (aluminum?) 4th wire from the 10-3 is connected to what the breaker panel sticker says is the ground bar and which is bolted to a big cable that is clamped to the water main at the other end like Mr. Home Depot said.
The thing is, the ground bar and the neutral bar, as far as I can see, are bolted together -- and are clearly designed to be based on how they're shaped. Unless there's some hidden insulation between them, it seems the neutral bar is grounded, and the grounding bar is... really another neutral bar?
I don't see anywhere in the panel (30 years old at least) to connect an additional grounding bar (no screw holes implying 'ground bar goes here'). The manufacturer's sticker in the breaker door says which one of those two bars is the neutral and the other which is the "ground if nec". Mr. Home Depot said I should assume electricians ignore all breaker panel stickers and just follow the grounding cable.
If I connect the 4th wire to the existing grounding cable or even run a new wire to the water main pipe, it seems logical to me that it will still be connected to the connected grounding and neutral bars.
An electrician told me off the record that everything is grounded anyway because a neutral wire is also a grounding wire, the usefulness of a dedicated grounding line is a myth, so just make sure your hots and neutrals are wired correctly at the breaker and the grounding wire won't make a difference, even if it's disconnected.
So kindly help me with this: do I need to rewire something -- either this circuit, this 4th wire, the whole panel, the neutral bar, should I not worry about it, etc... thank you for any advice you can give.
I'm installing a 30a 2-pole breaker in my breaker panel to be a dedicated line for a clothes dryer. The panel is Square D type QO with 100a main breaker and 20 breaker slots.
Clothes dryer manual says to use 10-3 cable, make sure to connect that 4th wire to the ground bar, or use 10-2 with a grounding strap and clamp that to a grounded object.
Home depot expert says the ground bar in the breaker panel is the metal bar with a cable bolted to it that terminates into the water main.
I used 10-3 and now have the black and red wires connected to the 2-pole breaker, and the white wire connected to the neutral bar where all the other white wires in there are connected.
The skinny, uninsulated (aluminum?) 4th wire from the 10-3 is connected to what the breaker panel sticker says is the ground bar and which is bolted to a big cable that is clamped to the water main at the other end like Mr. Home Depot said.
The thing is, the ground bar and the neutral bar, as far as I can see, are bolted together -- and are clearly designed to be based on how they're shaped. Unless there's some hidden insulation between them, it seems the neutral bar is grounded, and the grounding bar is... really another neutral bar?
I don't see anywhere in the panel (30 years old at least) to connect an additional grounding bar (no screw holes implying 'ground bar goes here'). The manufacturer's sticker in the breaker door says which one of those two bars is the neutral and the other which is the "ground if nec". Mr. Home Depot said I should assume electricians ignore all breaker panel stickers and just follow the grounding cable.
If I connect the 4th wire to the existing grounding cable or even run a new wire to the water main pipe, it seems logical to me that it will still be connected to the connected grounding and neutral bars.
An electrician told me off the record that everything is grounded anyway because a neutral wire is also a grounding wire, the usefulness of a dedicated grounding line is a myth, so just make sure your hots and neutrals are wired correctly at the breaker and the grounding wire won't make a difference, even if it's disconnected.
So kindly help me with this: do I need to rewire something -- either this circuit, this 4th wire, the whole panel, the neutral bar, should I not worry about it, etc... thank you for any advice you can give.