View Full Version : Another Blowing Furnace Transformer !


litefog
Nov 19, 2008, 04:16 PM
Furnace: Carrier Downflow-Gas 58DRC, circa 1988

First symptom of problem: Blower would not shut off after heating cycle

What has been done so far:

Bypassed the limit switch and a fusible link to see if that was what kept the blower on. Blower stays on, so they appear OK.

I then test the control board transformer's primary and secondary leads with a multimeter. I find there is an open winding on the primary side. So I replace the transformer (120v-24v) and turn back on the power. When I set the thermostat to call for heat, I hear the transformer sizzle. It's dead.

I have now replaced with another new transformer with an inline 3 amp fuse on one of the secondary leads.

I have also checked for loose & broken wires, no luck.

What should I do now to isolate the problem?

juggallojed
Nov 19, 2008, 06:39 PM
Well disconnect everything and try one circuit at a time.

Having no 24 volt will cause the fan to run so that is normal. Check the ohms on the gas control and the rest of that circuit.

KISS
Nov 19, 2008, 07:09 PM
If you want to get fancy. Get two 12 V brake lite bulbs and wire in series and place in series with secondary. Pull wires until the light goes out.

litefog
Nov 20, 2008, 06:01 PM
Guys, thanks for your replies!

Conclusion:

It dawned on me that when I bypassed the fan limit switch to see if it would shut off the blower, the transformer was already blown. I never checked the switch with a "good" transformer. Anyhow, replaced the fan limit and all is working well!

Question:

Why would a bad limit switch cause a transformer burn out like that?

KISS
Nov 20, 2008, 06:17 PM
Depends on how it's wired.

mygirlsdad77
Nov 20, 2008, 06:19 PM
If you want to get fancy. Get two 12 V brake lite bulbs and wire in series and place in series with secondary. Pull wires until the light goes out.

What ever happened to keep it simple stupid.lol

mygirlsdad77
Nov 20, 2008, 06:21 PM
Bad limit most likely didn't cause the transformer to burn up.

litefog
Nov 20, 2008, 06:33 PM
bad limit most likely didnt cause the transformer to burn up.

I would agree... though the transformer fuses stopped blowing once the switch was changed.

mygirlsdad77
Nov 20, 2008, 06:35 PM
Have seen stranger things. Hope all works well for years to come. Take care

Wouldn't mind if you rated me

hvac1000
Nov 20, 2008, 07:42 PM
Some fan and limit controls have both the 120 volt blower circuit and the 24 volt low voltage limit circuit in the same control. It could be possible to jump the wrong wires and toast the transformer or the internal switching created a short taking out the transformer..

T-Top
Nov 20, 2008, 08:19 PM
Did you remember to cut the jumper on the new fan limit control if the control is using 24v limit for one side and 115v for blower operation. If not your sending a 115v to the 24v side.

hvac1000
Nov 20, 2008, 08:55 PM
They are supposed to read the directions that come with the part. Woops I forgot no body reads the directions. LOL I am sure by now if it was a problem there would be another post but it is a very good reminder about that jumper. I missed that part.