PDA

View Full Version : Furnace Kicks on But doesn't Move Air


npb575s
Nov 16, 2008, 08:05 PM
I have a natural gas furnace that will kick on and I can hear the burners light, but it will not cirrculate the air ( I can turn the fan on using my thermostat) Any Ideas on what I need to do? Thanks in advance

npb575s
Nov 16, 2008, 08:30 PM
After reading some more posts I found that the error code that this heater has is an ignition failure, I can see the heating element heat up and the system tries this three times and then gives me this error. What would be my next troubleshooting task? Thanks again for any help.

hvac1000
Nov 16, 2008, 10:47 PM
Brand of unit?
Exact Model number of unit?

npb575s
Nov 17, 2008, 06:49 AM
There isn't a model or brandname on this system, I just bought this house in may, the only other thing that I do know is its an 80+ system. Sorry and thanks.

hvac1000
Nov 17, 2008, 03:09 PM
Since no info is available the best guess would be a defective fan and limit control OR the control that activates the blower in the heat mode. There can be various types of switches that can accomplish this and in some units the circuit board controls the blower also.

npb575s
Nov 17, 2008, 07:58 PM
Shouldn't the furnace still light the gas even if the blower doesn't kick on? When I turn the fan on my thermostat to on the blower does kick on. Is it possible that it is the gas valve?

hvac1000
Nov 17, 2008, 10:53 PM
From your first post!

I have a natural gas furnace that will kick on and I can hear the burners light, but it will not cirrculate the air

Now you say

Shouldnt the furnace still light the gas even if the blower doesnt kick on?

I am confused by your posts.

npb575s
Nov 18, 2008, 06:49 AM
Sorry about that, The burners do not light. Thanks for all the info too.

hvac1000
Nov 18, 2008, 07:08 AM
Problems of this nature can be brand and model specific. By law there has to be a model number and brand name on the equipment. Otherwise it is just a very bad guessing game.

letmetellu
Nov 18, 2008, 10:30 AM
I think the problem is the flame sensor So hvac1000 why don't you advise him on how to handle this problem, if you agree that it might be the flame sensor.

npb575s
Nov 18, 2008, 11:46 AM
I think the problem is the flame sensor So hvac1000 why don't you advise him on how to handle this problem, if you agree that it might be the flame sensor.

If that is correct, I think that I see were its located, and if I'm not mistaken from the other posts on this site I need to pull it out and clean it with steel wool or copper wool. I am also trying to get someone to come and look at it, if I can't resolve it with your guys help. Thanks again to all that are helping.

hvac1000
Nov 18, 2008, 12:43 PM
Sounds like he has a handle on the flame sensor cleaning.

npb575s
Nov 18, 2008, 05:15 PM
Problem found by HVAC Tech. the upper limit switch. But he didn't have one. Are these made to trip by a certain temp? Is it possible to swap the upper and lower temp? There again I am no expert to HVAC. Thanks for all the great advice.

hvac1000
Nov 18, 2008, 05:19 PM
Are these made to trip by a certain temp?

Yes

Is it possible to swap the upper and lower temp

NO do not try and swap. The one that is out is a safety device.

These parts are available. What are all the part numbers on the switch and the temp numbers. Also give a description.

npb575s
Nov 18, 2008, 05:33 PM
Are these made to trip by a certain temp?

Yes

Is it possible to swap the upper and lower temp

NO do not try and swap. The one that is out is a safety device.

These parts are available. What are all the part numbers on the switch and the temp numbers. Also give a description.

Thank you very much for your help. I have found the part and ordered it from a online vendor the total cost was about 16.50. Again thanks to all that have helped.

mygirlsdad77
Nov 18, 2008, 05:43 PM
Strange, usually when the high limit trips, it will cause the blower to come on, but you say the blower will never come on unless you turn it on at the stat? I do believe we will be hearing more about your problem.

npb575s
Nov 18, 2008, 06:01 PM
What other problems do you think that I might have? The part I'm replacing is a goodman
b1370154.

hvac1000
Nov 18, 2008, 06:11 PM
That is a roll out switch it is a safety device. If the new one trips you have another problem.

mygirlsdad77
Nov 18, 2008, 06:14 PM
Does the flame ever actually come on at all, even for a few seconds? Or do you get no flame ever.

mygirlsdad77
Nov 18, 2008, 06:28 PM
Its hard to tell what the tech meant by upper limit. I would think he meant high limit. Could have meant rollout switch. Could be a limit on the blower squirall cage. I guess, for the cheap part advised by the tech, I would start there, hope it takes care of your problems. Just let us know how it turns out.

MarkwithaK
Nov 18, 2008, 08:48 PM
We can't be certain that it even has a flame sensor since the OP didn't offer any real information. Could have a thermocouple or *shudder* a smart-valve.

If it does have a flame sensor then the burners would lit but quickly go out. A dirty/faulty sensor will not prevent the unit from firing, only from sustaining the ignition.

MarkwithaK
Nov 18, 2008, 08:50 PM
Never mind. I didn't read all the responses.