I have a 80% GMH8 goodman furnace that won't ignite. I can manually light it when the gas valve opens and it will run fine and shut off like normal. The glow plug ignitor doesn't come on but a couple of times I have saw it glow for a sec then go out way before the gas valve opens. The furnace was recently installed and we had to put a new circuit board in it when we installed it in the summer. Could it be the ignitor even though its came on a for a sec a few times? Any help would be greatly appreciated!

mygirlsdad77
Nov 10, 2008, 08:51 PM
Welcome back rocky, I believe you may have a faulty glow plug. You can light it manually every time yes? If so , you most likely have a bad glow plug, kind of like a light bulb that work once in a while, or (hopefully not) a bad control board. Lets hope for some more input on this subject,

Hvac, are you out there,

rocky21
Nov 10, 2008, 09:19 PM
Yes you can manually light it every time with no problem.

mygirlsdad77
Nov 10, 2008, 09:28 PM
Remove glow plug, look at it very closely, if there is a very white spot on the plug, or you see any gap(crack) on the plug, you need to replace glow plug.

rocky21
Nov 10, 2008, 09:48 PM
I pulled it out and I can't see and bad areas on it, it actually looks like new, could it still be bad even though there isn't any obvious damage?

wmproop
Nov 10, 2008, 09:56 PM
I`ve never had a igniter to work once in a while or even for a sec. once in a while,, you can do a continuity test on it, if it looks good and tests out,could be something isn`t telling it to ignite

rocky21
Nov 10, 2008, 09:58 PM
Is there anything other than the board that would tell it to ignite?

wmproop
Nov 10, 2008, 10:05 PM
Is it flashing a code at the board?if the pressure switch doesn`t since enough negative. Pressure it will not allow it to ignite

MarkwithaK
Nov 10, 2008, 10:06 PM
There is a slight chance that the HSI does have a hairline crack but still have continuity. When voltage is applied the HSI could vibrate ever so slightly but enough to break that continuity. It's a slim chance but I have seen it.

MarkwithaK
Nov 10, 2008, 10:08 PM
is it flashing a code at the board?if the pressure switch doesn`t sinse enough neg. pressure it will not allow it to ignite

If the pressure switch wasn't making then the valve wouldn't open and the poster mentioned he could ignite the unit manually.

wmproop
Nov 10, 2008, 10:14 PM
If the pressure switch wasn't making then the valve wouldn't open and the poster mentioned he could ignite the unit manually.

Right,, needed to re-read the post,, yes I did,, but still doesn`t seem right that the gas valve is opening up without the igniter lite first

MarkwithaK
Nov 10, 2008, 10:18 PM
right,,,,needed to re-read the post,,,,,,yes I did,,,,,,,,,,,,,,but still doesn`t seem right that the gas valve is opening up without the igniter lite first

That is typical sequence of operation. The HSI gets voltage and the valve will open if the igniter works or not. If the unit doesn't fire then that is what the flame sensor is for. No flame sensed then the valve is closed.

rocky21
Nov 10, 2008, 10:28 PM
Yes after it goes through the ignition cycle a couple times the light on the board does flash, it's a slow continuous blinking. And yes it does run fine after I manually light it with a bbq lighter.

hvac1000
Nov 11, 2008, 02:17 AM
rocky21

(((Here is a post from the same problem you had on Oct 18-19 2008)))

rocky21 https://www.askmehelpdesk.com/images/statusicon/user_offline.gif
New Member
Join Date: Oct 2008
Posts: 17
https://www.askmehelpdesk.com/images/reputation/reputation_pos.gif


i have determined that the problem lies with the glow plug ignitor. i did see it glow once when it was trying to cycle but as quick as it came on it went out and it seemed like it came on too early. if you manually light it it will cycle just fine, runs till the desired temp and shuts off normally.


Now you are back on Nov the 11th with the same problem?

What is up with this? I am sure by now you have replaced the ignitor you said was the problem back in the older post.

Here is a link to your older post first page.

https://www.askmehelpdesk.com/heating-air-conditioning/gmh8-goodman-furnace-wont-ignite-270833.html

rocky21
Nov 12, 2008, 06:08 PM
No I called the installer as was suggested, but it's a warranty issue and he doesn't have time to do warranty work for free, so its still not working. Just trying to get it back in working order.

wmproop
Nov 12, 2008, 07:10 PM
no i called the installer as was suggested, but its a warranty issue and he dosent have time to do warranty work for free, so its still not working. just trying to get it back in working order.



Doesn`t have time!! I`ll bet he had time when he was standing with his hand held out for you to fork over the big money when you got installation done,, most do have to charge labor but the part under warranty doesn`t cost him anything,, sorry but its people like that ,that gives the HVAC contracters a bad name ,

rocky21
Nov 12, 2008, 07:58 PM
I know and after spending so much money I'm just trying to save and fix it myself, I work on cars houses just about anything I can fix if I study it a bit. Should I get another ignitor and try that or do you think it might be the board again, or could it just be a bad connection somewhere?

hvac1000
Nov 12, 2008, 11:07 PM
Check your connections. If you have not replaced the ignitor check to see if voltage is available to the ignitor when the heat is called for. If power is available and the ignitor does not glow then it has to be defective.

mygirlsdad77
Nov 13, 2008, 04:44 PM
Hvac said it. Check for 120v at igniter, if 120v and no glow, replace glow plug. If no, or low voltage at glow plug, sounds like a connection, or board. Do you have any idea how to check for correct voltage at igniter?

How old is your furnace. If it is less than a year, the installer should fix any problems for free. If over a year, you will only pay for labor. Either way, you had a lousy company install your furnace, if they say they are to busy to take care of a heat call. They shouldn't be installing furnaces is they can't make time to work on them. Just an opinion, but I'm sure most would agree with me.

rocky21
Nov 13, 2008, 08:44 PM
I'm not 100% sure on how to properly check the voltage, I do have a multitester, not real sure what setting to set it on or how to check it properly. And yes the furnace is less than a year old it was started in the beginning of July and finished instillation about the middle of August.(yes it seemed like a long istall to me too)

mygirlsdad77
Nov 14, 2008, 06:03 PM
If you are not sure how to properly test power( or use a multimeter) then you need to demand that the original installer come and fix your problem. Call them every hour on the hour until they get their worthless selves out to fix your problem. Fact is , most likely they are installing furnaces, and don't have a clue as to how they work. Therefore they won't come work on it because they don't know how to trouble shoot it.

If you have a friend that knows how to read a electrical schematic, and is handy with a multimeter, then have them sit at your computer, and we will help them solve your problem.

mygirlsdad77
Nov 14, 2008, 06:04 PM
Does any one here agree that the poster got screwed by the installer?

MarkwithaK
Nov 14, 2008, 06:34 PM
no i called the installer as was suggested, but its a warranty issue and he dosent have time to do warranty work for free, so its still not working. just trying to get it back in working order.

Call him back and demand that he stand by his work. If he still refuses and will not come out the same day then inform him that you will report him and his company to the better business bureau. A warranty is not to be based upon his convenience.

mygirlsdad77
Nov 14, 2008, 06:37 PM
Mark is exactly right. There is no excuse for not working on a warrantied furnace. NO EXCUSE

hvac1000
Nov 14, 2008, 08:02 PM
I also agree with MarkwithaK but it makes me wonder how customers think sometimes unless there are circumstances we do not know of.

rocky21
Nov 15, 2008, 10:18 AM
Thanks for all of the help everyone, I appreciate your efforts, but I really need to get this going so I think I'm going to first call goodman direct and tell them about my problem since it is under warranty and to also let them know about the installer. I was manually lighting it last night again and it glowed for about 2-3 seconds but went out before the gas valve opened. So I'm kind of thinking the ignitor is good because if it had a break in the ignitor itself it wouldn't ever come on. I'm no heating expert but after all of the posts I've read and advice I have got on here I'm thinking it must be the board although the had to replace the board when he installed it because it came with a bad board and we couldn't get power through the board. I'm thinking I may have made a mistake when I went with a goodman furnace, not to mention their installer

wmproop
Nov 15, 2008, 11:49 AM
I agree a mistake was made with the installer, but for your money you couldn`t have done any better than the Goodman. They are as good as the next. The Goodmans have been around to long and have sold to many units to be selling junk. The bad/unexperanced installer can make any brand of equipment have a bad name

rocky21
Nov 15, 2008, 04:21 PM
I suppose your right, it just doesn't seem right that a new furnace should have so many bad parts in it. When he installed it he replaced the board once that was bad as well as the switch that is behind the door, now I'm thinking it may have another bad board.

mygirlsdad77
Nov 15, 2008, 04:35 PM
wmproop is right. Goodman is a great brand of furnace. Its kind of like buying a new car(even brand new cars have an issue now and then). Don't blame the goodman, blame the person that doesn't know how to fix the goodman( goodmans are right at the top of the line as far as efficiency, purchase price, and warranty goes) also very few problems, and easy to work on.

Hvac made a good point about customers.

Is there something you are not telling us. We need all facts before we can truly understand your situation with the installer.

rocky21
Nov 15, 2008, 05:56 PM
I've told you everything and I agree the installer should man up and take care of the problem, but after several phone calls and getting the same answer that he's pretty busy and doesn't have time right now doesn't exactly fix the problem. Right now I'm just wanting to get the furnace back in working order, its not much fun having to manually light the furnace every time you want heat, including when the wife wakes you in the middle of the night because the house is cold.

mygirlsdad77
Nov 15, 2008, 06:21 PM
Ok. You can start randomly replacing parts(which will cost you a lot more than calling for onsite help), or you can call a different company to come out and fix the problem( you will have to pay for labor, but since your furnace is less than a year old, you will not have to pay for parts. I might even suggest sending the labor bill to the original installer. If original installer won't pay, take them to small claims court. End of story. You say they need to man up, yes, but you do too, you need to make them take care of business or they will run all over you. I truly hope all works out well for you. Good luck