is it advisable to size the capacitor bank as 30% of the transformer KVA rating? I assume KVAR=30% Transformer KVA

erson
Oct 13, 2008, 11:27 PM
It is because of the stored calories and carbohydartes which is not soluble during digestion, as called resins in our stomach

danar
Oct 14, 2008, 04:14 AM
From your power angle formula you can size your capacitor depends upon how much power factor you are going to correct..

Debasis Roy
Feb 15, 2013, 08:28 AM
The total connected load both inductive and resistive in a plant is around 130 HP What size of capacitor bank is to be installed to have a power factor around 0.90 ?

Debasis Roy
Feb 15, 2013, 08:30 AM
The total connected load both inductive and resistive in a plant is around 130 HP What size of Capacitor bank is to be installed to have a power factor around 0.90

hfcarson
Feb 15, 2013, 01:22 PM
Find a company offering "Dynamic" correction equipment. Dynamic equipment monitors your demand and follows it, so to speak, will save you more than a static capacitor bank.
The equipment distributors will do calculations for you, although I would prefer a good electrical engineer who is working for you without the vested interest of selling equipment.

sinnadurai
Feb 16, 2013, 12:19 AM
First measure the present pf,then from charts you can get Var required to correct to 0.9. If the load varies during duty/working hours connect a power analyser or datalogger to record I,V Hz, pf,harmonice,MD,THD etc and give it to a professional PFCC installer to give you a report and quotation for installation of a suitably rated PFC bank including harmonic filters,if required.