Oct 3, 2008, 09:14 AM
I'm adding a workbench with outlets outside and would like to know if the plan I've come up with would work.I will be starting from the breaker box with two 20amp breakers.
The first 20amp breaker will be hardwired to my air compressor onlly


The second 20amp breaker would wire into a ( GFIC )then into the first four plug outlet then would wire into the second four plug outlet also adding a overhead fluorescent light

So if anyone can let me know if this would work also what size wire I would need to run this would much help thank you.

Washington1
Oct 3, 2008, 01:40 PM
If 20amps will handle the load, then it sounds good to me.

You say outside: If the receptacles are going to be outside, then you will need to install the appropriate weatherproof covers, and in some areas weather resistant receptacles.

KISS
Oct 3, 2008, 01:52 PM
If this is a garage type area, it always makes sense to put the lighting on a separate circuit, so if a power tool dies, you still have lights which could prevent an injury.

Washington1
Oct 3, 2008, 04:03 PM
If this is a garage type area, it always makes sense to put the lighting on a separate circuit, so if a power tool dies, you still have lights which could prevent an injury.

Good point! I agree!

hedlok
Oct 4, 2008, 01:00 PM
AWG # 12 is the size you'd use for 20 A. if you are running this on the outside remember that the wiring method must be suitable for the use. Romex cannot be used if exposed to physical damage, weather and sun... UF is OK but hard to work with... PVC conduit is my favorite for running on the outside... be sure to use THHN or THWN #12 stranded wire if you're using conduit.

KISS
Oct 4, 2008, 01:19 PM
THHN cannot be used, because underground is considered a wet location.

hedlok
Oct 4, 2008, 01:59 PM
He never says he's going underground... I gave the choice of THHN and THWN in case his local supplier has only one or the other... please do not try to correct people unless you have the facts straight... your pomposity shows... believe me, KISS I am as qualified as you are to give advice on this subject.

stanfortyman
Oct 4, 2008, 02:20 PM
hedlok, chill out. I hardly think KISS was being pompous. He just made a simple mistake, that's all.

This is all a moot point any way. When was the last time any of you saw #12 like this rated just THHN?? Everything these days is dual rated THHN/THWN.

hedlok
Oct 4, 2008, 02:30 PM
'kay... sorry, bro

Washington1
Oct 6, 2008, 01:07 PM
hedlok said: PVC conduit is my favorite for running on the outside... be sure to use THHN or THWN #12 stranded wire if you're using conduit.

Sorry hedlok, but I believe Keep read you correctly. Maybe you just wrote it wrong--it happens!

Yet, what you wrote above is clearlying saying that the OP can run Thhn in conduit outside.

hedlok
Oct 6, 2008, 03:15 PM
Okay where did the questioner say he was running underground? Thhn is acceptable in conduit run outside. Only when it goes underground does the wet location kick in. he is running the pipe in his garage, no?

Washington1
Oct 6, 2008, 03:54 PM
You said outside??

Here you go:
THHN — Indicates a single conductor having flame-retardant and heat-resistant thermoplastic insulation with a jacket of extruded nylon or equivalent material. The wire is rated 90ºC dry only.

THW — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation. The wire is rated 75ºC wet or dry.

THW-2 — Same as THW except that the wire is rated 90ºC wet or dry.

THHW — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation. The wire is rated 90ºC dry and 75ºC wet.

THWN — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation with a jacket of extruded nylon or equivalent material. The wire is rated 75ºC wet or dry. THWN wire suitable for exposure to mineral oil and to liquid gasoline and gasoline vapors at ordinary ambient temperature is marked "Gasoline and Oil Resistant I" if suitable for exposure to mineral oil at 60ºC, or "Gasoline and Oil Resistant II" if the compound is suitable for exposure to mineral oil at 75ºC. Gasoline resistant wire has been tested at 23ºC when immersed in gasoline. It is considered inherently resistant to gasoline vapors within the limits of the temperature rating.

hedlok
Oct 6, 2008, 04:48 PM
I still don't get what the problem is running thhn in conduit above ground and outside... if the pvc is installed per mfrs instructions... glued and all boxes sealed... it is a dry location. Only when you go underground is there a wet location.