Sep 1, 2008, 11:23 AM
Hi!

I have a York HVAC system. Yesterday, the blower started turning off after a few seconds to a minute of running, then turning back on and off repeatedly every few seconds to a minute

I took apart the blower unit and cleaned it and put it back in (what a pain in the... ), making sure all the wires were replaced correctly. It ran OK for a few hours, but then started doing the same thing again; turning off after less than a minute of running and attempting to restart repeatedly.

This happens whether trying to heat or cool and doesn't change no matter what setting the fan is on (auto or on all the time). I noticed that the motor also gets fairly hot to the touch. The fan blades move easily and are still spinning when the motor stop running.

I tested the capacitor and it's good.

Is this an indication that the blower motor is bad? If not, what else could it be? If it is the motor, I would like to replace it, to save some expense... where can I get a replacement for a GE 5KCP39PG N812AS (1HP, RPM = 1075/3 speed, with capacitor 15/370)?

Thanks!!

Jason

hvac1000
Sep 1, 2008, 05:18 PM
How did you check the capacitor? If you do not have a dedicated capacitor checker your findings could be wrong.

The motor you have is probably a run of the mill unit. If it is a belly mount that is all you need to know besides the specs. Grainger or other HVAC suppliers have these motors in stock. You might also try to check Ebay.

Remember if you get a new motor you must buy a new capacitor specifically recommended by the motor manufactures in regards to capacity and voltage. DO NOT try to use the old capacitor.

kirkwoodians
Sep 2, 2008, 07:44 AM
I checked the capacitor resistance with a digital multi-meter and it checked out fine. I will make sure I purchase a new one with the new motor.

Jason

chrisgeorge
Oct 13, 2008, 09:44 PM
I have this motor.. new in a box.. willing to sell.. email me [email protected]