Have a whirlpool rf362lxsb pulled element and tested have on 123V I believe should have 240 so where do I go from here? Thanks
esquire1
Aug 12, 2008, 05:39 PM
Check the outlet and see it you have 240V there. If not check the breakers to see if one has tripped. Is this a new unit that has nwver worked since day 1? If so and you have 240V at outlet you should really talk to the store wher you purchased
Credendovidis
Aug 13, 2008, 02:12 AM
Whirlpool RF362LXTS Electrical Requirements
This range is manufactured with the neutral terminal connected to the cabinet. Use a 3-wire, UL listed, 40 or 50 amp power supply cord (pigtail); or if local codes do not permit ground through the neutral, use a 4-wire power supply cord rated at 250 volts, 40- or 50-amps and investigated for use with ranges.
Electrical Connection
To properly install your range, you must determine the type of electrical connection you will be using and follow the instructions provided for it here. Range must be connected to the proper electrical voltage and frequency as specified on the model/serial number rating plate. The model/serial number rating plate is located on the oven frame behind the storage drawer panel.
When a 4-wire or 3-wire, single phase 120/240 volt, 60 Hz, AC only electrical supply is available, a 50-amp maximum circuit protection is required (or, if specified on the model/serial rating plate, when a 4-wire or 3-wire single phase 120/208 volt 60 Hz, AC only electrical supply is available, a 40- or 50-amp maximum circuit protection is required), fused on both sides of the line.
:)
I hope this clears the questions you have. Just make sure to wire it properly !
Have a look here : Link (http://www.ajmadison.com/cgi-bin/ajmadison/RF362LXTS.html?mv_pc=gg&cm_mmc=Google_Search-_-Skus+-+Optimized-_-Whirlpool-_-rf362lxts%7C-%7C100000000000000281310&gclid=CJXS4eO4ipUCFQtWtAod1W3CZA) - Go to Info and Guides !
: