View Full Version : What size motor will converter run
 
 tandemsforus
Jul 23, 2008, 06:24 AM
Hi
 I have a rotary converter that turns single phase into three phase. The motor on the converter says it is 5 hp. How can I tell what size 3 phase motor it will run
 Thanks
 tkrussell
Jul 23, 2008, 11:08 AM
Best to consult the manufactuer of your specific unit.
 
Here is a link to one of the more popular ones, look for Rotary Converter Sizing Chart link at the bottom.
 
3 Phase Converter Info- Sales- rotary phase converter, static 3 phase rotary converters. (http://www.phaseconverter.com/)
 
If this is not your manufacturer, Google "Rotary Phase Converter".
 tandemsforus
Jul 24, 2008, 06:40 AM
Thanks tk
 I got the 5 hp converter used with a band saw I bought. It was used and has no manufacture named.
 I looked at the site you recommended. Very informative.  
 Here is the rest of my question. Maybe I should have asked it from the start.  I also have a planer that has a 7.5 hp 3 phase motor. Per the information I read, from the site, it says I need a 20 hp, 15kw converter for hard start applications.  Does that sound right to you? It takes a 20 hp , 15 kw converter motor to run a 7.5 hp  3 phase motor? The cost of the converter is $1495, I can buy a single phase 7.5 hp motor for $5-600 dollars. As I read the info it would be 1/3-1/2 the price just to replace the 3 phase with a single phase.
 KISS
Jul 24, 2008, 08:32 AM
See if there is a code letter on the nameplate.  Motors can draw 300-600% of their rating upon starting.  See: motorsanddrives.com - Locked Rotor Code Letters (http://www.motorsanddrives.com/cowern/motorterms6.html)
 
Taking 7.5  HP * 746 W/HP =~ 5,6 KVA (some conversions thrown in)
 
15 KVA / 5.6 is about 2.7 X, so it's a reasonable assumption.
 
Don't forget to consider the wiring requirements which includes capacity and breaker space and disconnects, labor and inspections in your calculations.