View Full Version : Grounding rods at remote buildings


rkison
Jul 15, 2008, 01:56 PM
I pulled a 100 amp subpanel from my house main to a workshop (2legs/neutral/grd) put did not grd rod the workshop panel. I believe I need to drop the grd from the main and add a grd rod; is that correct? Also, now I am adding a subpanel from the wokshop panel to another unattatched building. I believe I need to pull 2 legs plus neutral and ground rod that panel; is that correct?

Man, I learned a lot from all of your discussions!

Thanks,

rkison

stanfortyman
Jul 15, 2008, 02:20 PM
ANY detached structure with a feeder MUST have a grounding electrode.

DO NOT omit the ground wire run with the feeders. Keep it and keep the grounds and neutrals separate in the panels.