PDA

View Full Version : How do I install a new Honeywell RTH230B from Honeywell T8195B


roninsolis63
Jul 12, 2008, 11:53 PM
Good evening.

Our old thermostat was model T8195B which came with wires C,Y,W,R & G. has no rererence as to where they hook up. The new one RTH230B doesn't say where these wires go. I've removed the Rc/Rh jumper according the instruction manual. Nothing went on at all. What can I go

Thank you
Solis

hvac1000
Jul 13, 2008, 03:43 AM
Just in case you lost your directions I took the liberty to post them below


http://customer.honeywell.com/techlit/pdf/69-0000s/69-1800.pdf

All the wires are listed in the directions so I would read them to make sure you wired the thermostat correctly.

The only wire no listed is the C but it is only for the old clock transformer that you do not need to use with the new stat.

There is a toll free phone number in the instructions on the lower right side at the bottom. Call honeywell they will have your answer.

NOTE: There are a few setting that you will have to do. They are also described in the instructions.

HINT: RH and RC since you really only have a 4 wire system to start with you need to reconnect them.

BTW here is the old thermostat wiring so you can compare wiring.

http://customer.honeywell.com/techlit/pdf/69-0000s/69-0564.pdf