I'm installing a 240 volt electric baseboard heating system that has a total watts of 5,000. A 2500 and a 1500 watt unit will each have their own wall thermostat. Then there will be two 500 watt units each with their own unit mounted thermostat. I plan on using a 30 amp breaker and 10-2 wire. My question is, the units are spread out over quit a distance and I wondering if I can run 10-2 wiring to a central location and then branch off to each unit or thermostat with 12-2. Will this overload any wires and is it OK to put a junction box in the circuit like this?

Thanks

tkrussell
Mar 15, 2006, 01:55 PM
Yes you can splice the #10-2 at a junction box, and take off in two directions to the heaters. The total amps on the feeder to the box will be about 20-21 amps, the branches from the box will be lower, no fear of overloading.

Just be sure not to bury the junction box, as it will always need to be accessible.