I have built a work shop in my back yard, I want to put a sub box in the shed.
The shed is 2 1/2 ft. from my main breaker box. I plan on putting a 100 amp
Breaker in the main box to feed the work shop sub box. The sub box will have
Separate c/b's for all the circuit's but no main breaker. My question is do I have to have a separate grounding rod for the sub box even though the grounding rod for the main box is just outside, or can I use the same rod as the main box? If I must use separate rod how far apart do they have to be?

donf
Jun 18, 2008, 03:18 PM
Sorry, you need a separate Grounding rod and EGC.

BACLARSEN
Jun 18, 2008, 03:27 PM
Ok, How far apart do they have to be? Or does it matter?

KISS
Jun 18, 2008, 04:19 PM
I'd say it's the AHJ (Authority Having Jurisdiiction) call. Personally, I think the separate ground rod isn't necessary, but it's not my call to make.

I might consider a panel with a main breaker. The main one in the shed would act as a disconnect and your allowed to have two. The shed's breaker CAN be higher than the feeder.

stanfortyman
Jun 18, 2008, 06:58 PM
I'm with KISS. You certainly CAN use the existing rod if you can reach it.

You DO need a disconnect in a detached structure with a panel. A main breaker panel is by far the easiest way to achieve this.

BACLARSEN
Jun 19, 2008, 10:31 AM
Thanks for all the replies I think I will use the existing grounding rod. (kiss)