View Full Version : Contactor relay from fan on an a/c not receiving 24V


biton1
May 30, 2008, 05:41 PM
The fan and the compressor of my a/c do not work, it seems that the electric board is getting 24V in but it is not coming out to the contactor relay.

wmproop
May 30, 2008, 08:42 PM
If 24v is going in, but not coming out,, its time to replace,, are you sure you don`t have 24 volts at the contactor,, usually the 2 smallest wires that plug into the lower sides of the contactor,, be careful electricity bites hard and deep

T-Top
May 30, 2008, 09:21 PM
It will help if you can tell us the brand and model of the system. A lot of the newer systems will have time delays,high pressure switches,low pressure switches and thermal overloads. All of the previous can keep the contactor from getting 24 volts and closing.