Apr 25, 2008, 11:54 AM
I have a 200amp service panel for my house in Glendale AZ and want to install a 100amp sub-panel for my garage/workshop. The electrical panel is on the other side of the house from the garage and I already have about 15,000 feet of 12ga stranded wire. Is it possible to run a 2 inch conduit through my attic of underground around the house and put about 6 or 7 circuits in it? I know I will lose some amperage when there are a number of wires run in the same conduit but how much I don't know. Additionally, is it permissible to have a 60 amp breaker in my service panel to run power to my 100amp sub-panel? Any help would be great! Thanks
donf
Apr 25, 2008, 12:21 PM
You cannot use #12 AWG to carry 100 amps. #12 gauge conductors are only rated for 20 amps.
Since you did not give a physical length of run, I would suggest you use #2 Copper or #4 Al. as the feeder to your sub panel.
In truth, you need to give us a lot more info.
Washington1
Apr 25, 2008, 02:16 PM
donf said You cannot use #12 AWG to carry 100 amps. True, but in this case the OP will be serving the non-service rated panel with a 60A breaker.
Regardless, donf is correct. To add, we do need more information.
donf
Apr 25, 2008, 08:55 PM
"Additionally, is it permissible to have a 60 amp breaker in my service panel to run power to my 100amp sub-panel? Any help would be great! Thanks"
The answer is still no! By code, you cannot use an Over protection device lower than the amount of amperage you are going to carry in the Branch Circuit.
Driving too much current through an current over protection device like a Circuit Breaker, will cause the breaker to trip. Running excess current through a conductor will cause fire.
If you are going to pull 100 Amps off the panel, then you need an over protection device and conductors capable of carrying current.
Also, since you are taking this to a remote subpanel in a different building, you need to ground the subpanel at that remote building. The only way you can use the main panel is to keep the subpanel in the same building.
EPMiller
Apr 26, 2008, 02:41 PM
"Additionally, is it permissible to have a 60 amp breaker in my service panel to run power to my 100amp sub-panel? Any help would be great! Thanks"
The answer is still no! By code, you cannot use an Over protection device lower than the amount of amperage you are going to carry in the Branch Circuit.
Driving to much current through an current over protection device like a Circuit Breaker, will cause the breaker to trip. Running excess current through a conductor will cause fire.
If you are going to pull 100 Amps off the panel, then you need an over protection device and conductors capable of carrying current.
As I understand it, code does not say that you MAY NOT put a 60A breaker in your main panel, but if you do, the sub panel will only be capable of supplying 60 amps. The size and type of cable connecting the panels and the breaker in the main panel determine what you will be able to get from the sub panel.
Stratmando
Apr 26, 2008, 04:32 PM
You can easily run MANY more than 6 or 7 circuits of #12 through a 2" conduit. Would have to dig up Code Book, but NOT an issue.
A 60 Amp sub panel with #6's ,and #10 for ground.
Washington1
Apr 26, 2008, 07:41 PM
Additionally, is it permissible to have a 60 amp breaker in my service panel to run power to my 100amp sub-panel? Any help would be great! Thanks Now you are getting it. Yes, you can do this.
You can install a 60A breaker in your service rated panel to serve your non-service rated panel (Sub-panel). Yet, you cannot terminate a #12 or #10, or combination there of, and use it as feeder from a 60A breaker. You would have to use a # 6 or larger conductor as your feeder to your sub-panel.
tommybrown
Apr 27, 2008, 01:47 PM
Only ANSWER the question on this page here. Do NOT ASK a question.
You are NOT logged in.
tommybrown
Apr 27, 2008, 02:06 PM
OK, here is a little more detail. I live in Arizona and here the service panel is located on the outside of the house. My garage is attached and on the opposide side of my house from the service panel. My plan was to run #1 wire through 2in conduit under ground to feed a 100 amp sub-panel. I bought a bunch of 2in conduit and was planning to buy the wire when I found 3 5000 ft rolls of 12ga stranded wire at a yard sale on the cheap. One black one red and one white. So I changed plans and am now going to put the sub-panel right next to the service panel and run the 12ga wire through the 2in conduit through the attic to the garage. What I need to know is if I can run about 6 or 7 curcuits through the 2in conduit and what I need to do to supply power to the 100 amp service panel that I already have. I am not running anything into the attic that requires anything more than the 12ga wire. Maybe a 220 line for future tools or a welder. Thanks for any help.
donf
Apr 27, 2008, 02:23 PM
Tommy,
What part of NO don't you understand. You can not use a 12AWG conductor to carry 100 Amps. It is flat out not allowed.
Nor can you use a 60 Over protection device to pull 100 Amps from your panel. You can use a 60 Amp Over-protection device with #6 copper to route 60 amps to the garage, providing the run is short enough that you don't have to worry about any voltage drops.
You can use a dual 100 amp breaker with #2 copper to pull 120/240 off the panel and route it to your subpanel for re distribution in the garage.
By the way, the subpanel will have to be in the garage as well.
Stratmando
Apr 27, 2008, 03:18 PM
You can easily run MANY more than 6 or 7 circuits of #12 through a 2" conduit. Would have to dig up Code Book, but NOT an issue. Each would be on a 20 Amp circuit.
A Red and Black can share a Neutral, if they are on opposite phases, and breakers ties together. If you don't want to share neutral, pull 8 whites, 4 reds, and 4 blacks for 8 circuits, plus a #12 for ground. Take Care
You would need #4 copper for 100 Amps, aluminum would be larger.
tommybrown
Apr 27, 2008, 03:34 PM
I am not running 60 amps through 12ga wire. I want to put the sub-panel 4 to 5 feet from the service panel supplying power to the sub-panel with a #1 wire. Then from the sub-panel use the 12ga wire to feed the garage. Thank you Dorf for basically calling me an idiot. I understand I can't run 60 amps with 12 ga wire. Got it. I am simply trying to get you to understand what I need. Appearantly I am failing to do that. I just need to know what breakers and wire size I need to hook up the service panel? Now Dorf, you're saying I need to have the sub-panel in the garage. Why can't it be attached next to the main service panel?
Stratmando
Apr 27, 2008, 04:52 PM
Next to Panel is fine. #1 is Overkill/but fine, I have a habit of that.
Does my 5:18 post make sense?
tommybrown
Apr 27, 2008, 05:02 PM
Stratmando, yes your earlier post makes sense. Would you think pulling a permit would be required?
EPMiller
Apr 27, 2008, 07:23 PM
<snip>My plan was to run #1 wire through 2in conduit under ground to feed a 100 amp sub-panel. I bought a bunch of 2in conduit and was planning to buy the wire when I found 3 5000 ft rolls of 12ga stranded wire at a yard sale on the cheap. One black one red and one white. So I changed plans and am now going to put the sub-panel right next to the service panel and run the 12ga wire through the 2in conduit through the attic to the garage. What I need to know is if I can run about 6 or 7 curcuits through the 2in conduit and what I need to do to supply power to the 100 amp service panel that I already have. I am not running anything into the attic that requires anything more than the 12ga wire. Maybe a 220 line for future tools or a welder. Thanks for any help.
OK now things are a bit clearer. You want the sub panel right next to the main panel and then you are going to run 6 or 7 20amp circuits from that sub panel, through the conduit to the garage. My work does not use conduit, and I don't have my code book here, so I will have to defer to someone else on the exact count of #12 conductors allowed in a single 2" conduit. It sounds like you will have max 18 or 21 conductors if they are all 120 volt circuits or 240 volt with no neutral. Less if you share the neutral on 2 120 volt circuits on opposite legs (double breaker w/common trip). I believe you will have to have 1 green grounding conductor for each circuit, so you will have to buy that wire.
Stratmando (see above) is correct on your conductors between the main and sub panels, you will need four conductors for that. 2 hot, 1 neutral and 1 grounding. You will have to separate the neutrals and grounds in the sub panel on their own buss bars and the neutral bar must not be bonded to the panel. I question the single #12 ground wire for the seven circuits. However, I repeat, I work with romex, not conduit.
Washington1
Apr 27, 2008, 08:41 PM
Tommy,
Next time you post with a question, try giving as much information as possible in the beginning. This way we do not have so much confusion!
Thank you!
donf
Apr 28, 2008, 05:02 AM
Tommy,
I believe that the NEC tells us that the subpanel has to be inside the detached garage and it has to be grounded at the garage.
Right now I'm supposed to be in bed now, so I'll check the code on this a little later today.
Meanwhile, if anyone would like to cite the code section that does allow placement of the Sub-panel five feet from the main panel and then a 100' (?) of multiple branch circuits to the detached garage, I'd appreciate it.
Stratmando
Apr 28, 2008, 06:33 AM
When I mentioned NOT issue, The maximimum number of #12 THHN in a 2 " PVC is 98.
Maximum in EMT is 100 #12's. This is 40% fill.
Can't say about a permit in your area.
donf
Apr 28, 2008, 08:42 AM
Strat,
Since you are required to derate current carrying conductors by 75% if there are 3 or more "Currernt Carrying Conductors" within the conduit and Tommy is putting at least 6 or 7 current carrying conductors where are you going to place the derated over protection devices?
Am I missing something here?
It makes no sense to build the subpanel five feet from the SEP.
What does make sense is to pull the 100 amps off the SEP using #4 Copper conductors for the run to the garage wall (Assuming that you LRA allows you to place the sub-panel box on the outside of the structure) then set a Grounding rod for the subpanel and finish the installation.
If he runs it the other way, six or seven cables from the sub-panel (Next to the Main Panel) he has no access to the breakers in the event of an emergency. He's got to leave the garage to run completely around the other side of the house to get to the sub-panel.
Let's all hope there's never an emergency requiring a quick killing of the power to the garage!
Stratmando
Apr 28, 2008, 02:25 PM
Donf,
He may have run out of Breakers is likely why it is 5 foot away.
If the Panel was in the Garage it would be Convient, I am hoping he does not run into a lot of Tripping Breakers. Either way is fine. I am answering his question.
May not be an acceptable place in the Garage or have room? plus he has free #12. This will allow him to do less costly. If he was having Welders, compressors, something requiring other than single pole/20 amps, I may would suggest Sub in Garage.
Take Care
stanfortyman
Apr 28, 2008, 02:59 PM
This WHOLE thing is wrong from the get go, and for several reasons.
1) You CANNOT feed a detached structure with more than one circuit. For this purpose a multi-wire circuit is considered one circuit.
It is being proposed to run MANY circuits to this garage. NOT good.
I am still uncler if this is detached or attached. If it is attached then this does not apply.
2) Derating was brought up. For all practical purposes, over NINE CCC's (current carrying conductors) you must start to derate #12 THHN. It is involved as to why, but ten or more CCCs and you must derate to the point where you are under the "standard" 20 amps for #12.
Keep in mind, the neutral of a MWBC (multi-wire branch circuit) does not count as a CCC nor do grounds.
It is being proposed to run WAY more than nine CCCs.
For instance, if he runs ten MWBCs, for twenty circuits, this is 20 CCCs and he MUST derate those circuits to 50% of 30 amps, or 15 amps.
IF this is an attached garage, then you would have to run several smaller conduits with up to eight circuits, (even MWBCs) in each to allow each circuit to stay 20 amps.
I can understand trying to save money and using something you have on hand, but butchering a job and doing things ALL wrong is NEVER a good way to go.
If you are insistent on using the THHN you then have go the multiple conduit run route provided the garage is attached as I said.
I believe you will have to have 1 green grounding conductor for each circuit, so you will have to buy that wire.NOT true, you need ONE ground per raceway, based on the largest circuit conductor.
So you can have 100- #12 wires in a conduit and you would only need ONE #12 ground.
EPMiller
Apr 28, 2008, 03:26 PM
<snip>
NOT true, you need ONE ground per raceway, based on the largest circuit conductor.
So you can have 100- #12 wires in a conduit and you would only need ONE #12 ground.
Thanks Stanfortyman. I will file that fact for future reference if needed. :)
As to the original question, I think the garage is attached, and he did mention 6 or 7 circuits. That would be 12 or 14 CCCs, so he would get into derating unless he did the multi wire branch circuit setup.
EPMiller
stanfortyman
Apr 28, 2008, 03:48 PM
Heck, he could do four MWBCs in a 1" conduit and be all set.
donf
Apr 28, 2008, 05:34 PM
Strat, that makes no sense to me. I believe that he is limited to one supply cable into the detached garage. So that means one breaker off the SEP (100 amp - two phase) to supply 120/240 on the sub panel.
LRA has to determine if the sub-panel can be on the outside wall of garage.
All receptacles inside the garage need to be GFCI protected.
Tommy, it appears that you believe I think you to be an idiot. That is absolutely untrue. I don't know anything about you. If I appear to be rude, I apologize, I'm from Da Bronx, NY and we are speak two languages. Manhattan English and Bronx speak. I promise you I am not trying to be rude. My concern is that you are not approaching this situation wisely so I ask you questions first to determine what you know or don't know.
Stratmando
Apr 28, 2008, 06:00 PM
Had replied but didn't send post, but I said, "I thought it was attached, then reread
"through my attic of underground"? Others felt it was attached also. Myself it was confusing , and I should have asked him to clarify.
donf
Apr 29, 2008, 07:53 AM
Tommy,
I went back through all the postings and discovered that your garage is attached. That's a different ballgame. I was under the impression that your garage was detached. I apologize for my error.
I'll go back and start over.
donf
Apr 29, 2008, 08:18 AM
Strat,
The phrase, "through my attic of underground"? is a typo.
It should read, "through my attic or underground."
Washington1
Apr 29, 2008, 07:36 PM
Wow!