View Full Version : 100A 240v subpanel with #4 wire


Mauro
Apr 14, 2008, 03:06 PM
Hello, I have a 200 Amps main panel and i will install a subpanel 100 feet apart to run my new swimming pool pump, sprinkler pump and garden lights (maybe some other appliances to aliviate load in a 60 Apms existing subpanel)
Pumps will run in 220v.

I was told to put 2 #4 wires 1 #6 and 1 #8 on conduit pipe baried 1 feet underground.

Will this cable work for me? Alcan Stabiloy # 4 AWG S- E- R 4 - WIRE ??

Also i was told to use a Murray panel 100 AMP.

Thanks for any help or advice you can provide.

Mauro

stanfortyman
Apr 14, 2008, 05:02 PM
Will this cable work for me? Alcan Stabiloy # 4 AWG S- E- R 4 - WIRE ??

Not in conduit it won't. Or buried either.
You need THWN conductors in conduit the WHOLE way since this is a feeder to a pool panel.

Pools are no place to mess around. Are you familiar with all the codes involved??

Mauro
Apr 15, 2008, 04:03 PM
Thanks for your reply, I will do it with 3 #4 copper and 1 #6 inside 1" conduit as per my electrician advice.

Thanks again.