At 440 volts, What motor rating in KW I will use wye delta starter.

Credendovidis
Mar 29, 2008, 03:19 AM
at 440 volts, What motor rating in KW i will use wye delta starter.
Star/Delta Starters are required to be fitted on all motors greater than 4KW (about 5 HP).
The applied voltage is irrelevant. Only the power requirement is the official deciding factor.
Of course nothing holds you back to install it on any smaller 3 phase motor.
They are used to reduce the start current applied to the motor during start.

stanfortyman
Mar 29, 2008, 05:06 AM
at 440 volts, What motor rating in KW i will use wye delta starter.
I have NO idea what you are asking.
Regardless...


THIS IS NOT DIY WORK!!! CALL AN ELECTRICIAN!!!

mackycan
Jan 31, 2010, 11:59 PM
Star/Delta Starters are required to be fitted on all motors greater than 4KW (about 5 HP).
The applied voltage is irrelevant. Only the power requirement is the official deciding factor.
Of course nothing holds you back to install it on any smaller 3 phase motor.
They are used to reduce the start current applied to the motor during start.

As for me, I recommend him to use wye-delta starter for 7.5hp and higher. For < 7.5hp just use CB and inverter, or cb and contactor (you can't vary the speed though)...