Hello,
Lights in the hallway became real bright then blew out & a power strip melted.
Wiring in house is about 10-15 years old.
Did some investigation and here is what I found out:
The neutral wire in the subpanel for the lights was burnt and disconnected. The neutral wire is in 14/3 romex (ground,white, red, black).
The red & black wire are connected to circuit breakers opposite phases but not connected to a double pole breaker (breakers did not trip.
Since the neutral burnt and not connected to the neutral bar and the breakers did not trip and were still on, I put my volt meter to a receptacle and I got 240 volts between the hot and ground and my tester showed hot/ground reverse.
Got 240 volts at the switch box where the light bulbs blew.
I reconnected the neutral wire and turned on the first breaker. Checked lights and receptacles and all seems fine.
Turned off the first breaker and turned on the second breaker. Checked lights and receptacles and all seem fine.
I am afraid to turn on both breakers at the same time.
I am looking for the box with the other end of the 14/3 romex that comes from the sub panel.
Has anyone come across this problem or any suggestions?
Thank you in advance
Lights in the hallway became real bright then blew out & a power strip melted.
Wiring in house is about 10-15 years old.
Did some investigation and here is what I found out:
The neutral wire in the subpanel for the lights was burnt and disconnected. The neutral wire is in 14/3 romex (ground,white, red, black).
The red & black wire are connected to circuit breakers opposite phases but not connected to a double pole breaker (breakers did not trip.
Since the neutral burnt and not connected to the neutral bar and the breakers did not trip and were still on, I put my volt meter to a receptacle and I got 240 volts between the hot and ground and my tester showed hot/ground reverse.
Got 240 volts at the switch box where the light bulbs blew.
I reconnected the neutral wire and turned on the first breaker. Checked lights and receptacles and all seems fine.
Turned off the first breaker and turned on the second breaker. Checked lights and receptacles and all seem fine.
I am afraid to turn on both breakers at the same time.
I am looking for the box with the other end of the 14/3 romex that comes from the sub panel.
Has anyone come across this problem or any suggestions?
Thank you in advance