View Full Version : Can the CB in a subpanel exceed the ampacity of the CB in the Main Disconnect?
psherrill
Mar 4, 2008, 10:06 AM
Can the main breaker in a sub panel exceed the ampacity of main breaker in the primary disconnect?
stanfortyman
Mar 4, 2008, 01:52 PM
Yes. The main breaker in a sub-panel is merely acting as a disconnect. It's rating can be whatever you want since the breaker in the main panel is protecting the feeder.
Washington1
Mar 4, 2008, 09:15 PM
Not that I'm asking, but I'm sure someone is :)
Here it goes: So does this mean I can protect my 100A non-service rated panel in my detached garage, using a 60A breaker at my service rated panel?
:)
Simply asking a question you already answered :)
stanfortyman
Mar 5, 2008, 04:18 AM
Here it goes: So does this mean I can protect my 100A non-service rated panel in my detached garage, using a 60A breaker at my service rated panel? Yes, that is exactly what it means.