Feb 19, 2008, 10:00 PM
I work for a cable company and we have this phenomenon called voltage feedback. It breaks down into two parts. First part is we read an AC voltage between the coax and house ground, which we say is "floating voltage". Second part is where we grab the coax and touch the ground and get a "tingle". Sometimes we can attribute the tingle to a bad electrical plug, bad t.v. etc. but sometimes, none of these apply and we are baffled. Any more knowledge would be extremely heplful.

KISS
Feb 19, 2008, 11:50 PM
Touch the coax you mean - the shield side, correct?

The first thing your supposed to do, is create a ground before the cable enters the house, right

Guess where that ground is SUPPOSED to be?

The same place the electrical system is grounded, the telco system is grounded and the CABLE system is grounded. If it's the other side of the house, all bets are off.

You didn't say what the range of the size of the voltage was nor what the current is. Do you have any idea?

There is no question that there is a difference of ground potentials.

Let's think about what can cause that?

1) hot and neutral reversed on an outlet - big time problems
2) Leakage current in an attached device
3) Your ground is bad
4) The house electrical ground is bad
5) Your not grounded at the same point as the house.
6) If a computer and TV shared a surge supressor and the outlet has an open or intermittant ground, your in trouble.
7) A distribution amp
8) a cable modem especially ones connected by USB

I'll have to think some more?

I would:
Install your ground block (you know where it's supposed o go)
Install the system's cable
Measure V between house outer conductor and your conductor

If it's substantial then you have to ask?

Test #1: Is your ground at the house the same potential as the house ground with no cables connected to your ground block at the house?

Your not going to like what I say, but it will work. Go to the electrical service and run a wire from an exposed point to the location of your ground connection. Measure V between this wire and the outer shield of the house's connection.

That's the hard one if the voltage is large.

If it is small but you still have the voltage problem, then disconnect half of the coax cables inside. Exist/not exist, then pick the other half and use the binary search technique to find the culpret.

I'll think some more. Need feedback.

KISS
Feb 19, 2008, 11:59 PM
With my long wire test, you could use the voltage between your properly grounded ground block with nothing attached to the customer's side and the ground from an extension cord from the nearest electrical outlet with nothing plugged in.

erug
Apr 17, 2008, 11:12 PM
i work for a cable company and we have this phenomenom called voltage feedback. it breaks down into two parts. first part is we read an AC voltage between the coax and house ground, which we say is "floating voltage". second part is where we grab the coax and touch the ground and get a "tingle". sometimes we can attribute the tingle to a bad electrical plug, bad t.v., etc. but sometimes, none of these apply and we are baffled. any more knowledge would be extremely heplful.
I have no answer - I have the problem. Our cable tech said that our TV is sending voltage back into our cable box - 50+V on each of the video cables! I would love to know that there is something out there that would absorb the voltage between the video cables and the cable box..,. or some way to ground the TV - it only has a 2 prong cord. Any thoughts?

KISS
Apr 18, 2008, 05:13 PM
With so many different standards, I'm having a lot of trouble with the term "video cables".
Describe them?

Does one of the ends look like this? http://images1.hdpi.com/product_thumbnail/philips-PH61025.jpg

Is the TV connected to a surge suppressor?

Is a surge suppressor used on the same circuit, but in a different room?

Any three prong plugs plugged into this circuit even in other rooms? if so, what kind of devices?

donf
Apr 18, 2008, 07:26 PM
The correct solution is to call the tech's manager or corporate manager and as for an on-site visit by a local engineer to find and correct their problem.

Unless I've forgotten how TVs work, they are receivers and it is very unlikely that they would emit a backwards emf (static) let alone a 50V+/- charge.

What happens when you disconnect the cable that supplies the TV from the cable receiver, apart from the loss of picture.

I suspect that there is a dirty frame ground or a floating frame ground with the cable box. Ask the tech to change it out ans see if the voltage is still present on his end of the cable.

buzzman
Apr 18, 2008, 07:47 PM
That floating neutral problem is caused from having your power source ungrounded. Whenever you have a reading like this, (Voltage between ground and neutral). What happens when loads are applied to an "ungrounded system", it causes the "phase voltage" to try and balance itself, since it has no reference to ground. Remember the circuit will try to balance itself if you do not give it a reference point to ground. One way of checking this is to slowly take loads off the power source and note the voltage readings between neutral and ground. As the loads are taken off, the voltage slowly should read closer to zero between ground and neutral or in this case, the coax and ground. Whenever you have this problem, always check to make sure your source has a "grounded neutral". This will keep the "zero" point from shifting as you apply load.

KISS
Apr 18, 2008, 08:05 PM
Another way, which I have seen is a defective ground in an outlet and devices with switching power supplies and RFI filters attached. The RFI filter dumps energy onto the ungrounded ground raising the ground potential of everything connected.

That can cause no problem until you connect to a real ground which could be the coax or could be the TV. Open grounds and neutrals can even occur with defective outlets. I saw one outlet which would loose it's ground when both plugs were used.

That's why I'm asking questions.

KISS
Apr 20, 2008, 10:08 PM
buzzman:

I have SEEN it happen. This is not theoretical.

Computer had a grounded outlet and used a switching powersupply with an RFI filter.

The computer was plugged into an outlet strip with other devices.

The ground was defective in the outlet.

There was about a 70 VAC potential between the ground of the outlet strip and a nearby properly grounded outlet.

The computer (was a micro-computer at the time) died because it communicated with a properly grounded device.

When the outlet was removed and disassembled, the ground bar had sparks marks and it was a pressure fit with no fasteners. BAD GROUND, not a BAD NEUTRAL in this case!!

buzzman
Apr 21, 2008, 07:22 AM
buzzman:

I have SEEN it happen. This is not theoretical.

Computer had a grounded outlet and used a switching powersupply with an RFI filter.

The computer was plugged into an outlet strip with other devices.

The ground was defective in the outlet.

There was about a 70 VAC potential between the ground of the outlet strip and a nearby properly grounded outlet.

The computer (was a micro-computer at the time) died because it communicated with a properly grounded device.

When the outlet was removed and disassembled, the ground bar had sparks marks and it was a pressure fit with no fasteners. BAD GROUND, not a BAD NEUTRAL in this case!!!

There is no doubt grounding can do weird things... Thanks for the details. I myself have seen things similar and it has come down to soil testing to assure "zero potential" existed. I was involved with the relocation of a service ground to a different area because of a high resistivity problem. Improper ground plays havic in electronic equipment because it is so reliant on its reference point.

retsoksirhc
Apr 21, 2008, 07:33 AM
Probably of no use to this discussion, but interesting nonetheless:

We had voltage come back from Satellite receivers that, for some reason or another, customers would connect to cable outlets after the initial installation. I just don't understand what people are thinking sometimes...

KISS
Apr 21, 2008, 07:45 AM
You know that there are systems out there which use 2 grounds and use green and green with yellow stripe.

Green is protective ground
Green with yellow is signal ground.

And they tend to keep them separate.

Motors would use protective ground.
The other receptacles would be the orange independent ground and connected to signal ground.

buzzman
Apr 21, 2008, 09:36 AM
You know that there are systems out there which use 2 grounds and use green and green with yellow stripe.

Green is protective ground
Green with yellow is signal ground.

And they tend to keep them separate.

Motors would use protective ground.
The other receptacles would be the orange independent ground and connected to signal ground.
This is called an "Isolated ground system". The different color wires are used to differentiate the two grounding sytems. It is a separate path of ground isolated from the main grid, that goes to the same grid, if that makes sense... lol. In other words, it will have its own "strict path to ground" that will not be tied in parallel with any other operating system ground. It is used to take away "circulating currents" in Electronic wiring that is often installed close to or around other sources of energy. These circulating currents can cause variations (Misreadings) in electronic devices when accuracy is of upmost importance. Ie: Instrumentation in an airplane, gas plant,. etc...